HI ALL
we are using caterpillar sr4 600kva generators as the power supply for mechanical drilling rig. they are 2 generators but we use one at time. the maximum load is about 450amps.we need to do synchronizing to change over between the generators. i tried but they are not sharing the load, one of them is carrying 300amps and the other is 100amps. both generators have caterpillar VR6-B voltage regulators. each regulator connected to droop CT and to minimise the circulating currents flow between the generators i have to connect X connection between both droop CTs leads ''cross current compensation'' as per regulator manual. this connection has to be on when both generators are online and off when only one of them is online, so the wire has to pass normaly open contacts in series for both generators main breakers. my question is if i just connect them without passing the contacts ''always connected'' ''two droop CTs on parallel'' is this will effect operation of the generator running alone?
also i have another question: droop CT terminals at the regulator are 3 ''one is common and one is for 1amp CT and the third is for 5amp CT'' so it depends on the CT you are using if it is 1amp output or 5amp output. i am using the original CTs came with the generators.
my question is: is the droop CT for caterpillar SR4 generators 1amp or 5amp output? i am connecting it as 1amp output CT, and maybe it is not. maybe thats why the generators are not sharing the load.
any reply will be appreciated.