04/04/2008 3:05 AM

Hi Cr4 Gurus,

I would like to ask a question regarding power saving. The plant i am working in is a Chemical plant, we are in the phase of crisis. as a measure of cost saving we need to deal the task of power saving which goes upto 1 Lakhs per month.

What can be done for improving energy efficiency

thnx and regards

Register to Reply
User-tagged by 4 users
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#1

Re: Energy saving

04/04/2008 5:37 AM

Mostly commonsense things: switch off lights and airconditioning when not in use, set the airconditioning temperature only as low as is necessary to feel comfortable unless the process really requires such low temperatures, switch off equipment when not in use, open curtains or blinds to let in natural sunlight so that you can switch off a few lights, cut off power to the conference rooms when the top management are having a meeting so as to force them to cut the meeting short and prevent them overheating the plant with their vented hot air (note: last suggestion NOT to be taken seriously). Whatever you do, NEVER switch off your air scrubbers or wastewater treatment plants unless there is really no production going on.

__________________
If only you knew the power of the Dark Side of the Force
Register to Reply
2
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#2

Re: Energy Saving

04/04/2008 10:11 AM

One big one is to operate your electric motor driven equipment, particularly pumps, on their best efficiency point. Operators are notorious for not being concerned about how they operate pumps, which decreases the reliability and increases energy consumption.

The other common practice is that if you have spare machines operators will operate two at 50% instead of one at 100%. This makes them more comfortable since if they loose one the second takes up the slack quickly, but this is a terrible waste of energy as well.

A third one is if you have electric motors that run hot due electrical problems, then pull them out and replace them. Every joule that goes to heat is one that is not used efficiently to drive the equipment and is electricity wasted..

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2008
Location: N. Texas, U.S.A., et al from time to time.
Posts: 155
Good Answers: 3
#3

Re: Energy Saving

04/04/2008 6:43 PM

bmadhu srao

You could do worse than review the energy savings programs of the newer U.S. Independant School Districts in pro-green progressive cities. Installing light wells to reduce the need for artificial light. Remodel roofs and install growing green cover and shaded roof top garden access for break areas with mist coolers if water is cheap. Air chambers at entrance/exits. Evaporative intake air pre-cooling towers for mechanical Air Conditioning with heat exchangers for potable water pre-heating. Deciduous shade trees and vines on south and west sides of buildings. Solar screening on south and west exposure windows in summer. Earth berms on first floors up to window lines. Use of insulated bunker saline water tanks to store chilled brine during night-time off peak, cheaper commercial electrical utility rates for reduced daytime operational expense during peak day hours...

That should get your clock ticking for starters

__________________
The apparent cycles of action are: Start, Change, Stop. The true cycle of action is: Create, create, create, etc.
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#4

Re: Energy Saving

04/04/2008 7:22 PM

I suggest investing in solar power. Photo-galvanic power is dropping per watt. Heating water (or other liquid) is well proven.

__________________
Bob
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#5

Re: Energy Saving

04/04/2008 8:53 PM

In a chemical plant the electricity to run the lights in the offices is just a small fraction of the power used. So while these are nice ideas, they are not going to make much of a dent in his power bill...

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#6
In reply to #5

Re: Energy Saving

04/04/2008 11:04 PM

Why would he be limited to using the electricity for the lights?

__________________
Bob
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#12
In reply to #6

Re: Energy Saving

04/05/2008 4:54 PM

Because when you are using enough electricity to power a small town like this chemical plant usually does, photovolaics are not going to be a cost effective investment, and skylights and such will make no measurable impact on his electric bill at all.

On the other hand conserving energy by running his equipment effeciently will probably save him 20 to 30% of his current bill.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#13
In reply to #12

Re: Energy Saving

04/05/2008 11:26 PM

My knowledge of chemical plants is minimal at best. My thoughts were more general in nature. It seemed that the larger the building size the more roof area exposed to the energy of the son.

__________________
Bob
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#14
In reply to #13

Re: Energy Saving

04/06/2008 7:26 AM

Here is a picture of a chemical plant. There are not many buildings at all, just lots of pipes, reactors, and pumps...

One other thing that can be done is to turn off some of the lights in the process areas, but that can pose a safety hazard...

Register to Reply
Power-User

Join Date: Mar 2008
Location: N. Texas, U.S.A., et al from time to time.
Posts: 155
Good Answers: 3
#18
In reply to #14

Re: Energy Saving

04/12/2008 10:38 PM

After a look at a "typical" chem plant, I would say that retrofiting with low energy LED light technology would make a significant percentile difference.

__________________
The apparent cycles of action are: Start, Change, Stop. The true cycle of action is: Create, create, create, etc.
Register to Reply
2
Commentator

Join Date: Jan 2008
Posts: 67
Good Answers: 6
#7

Re: Energy Saving

04/05/2008 12:25 AM

By the way I lived in India for three years, hope this is a little pay back.

Consider the following

Is the cost increased due to change of rates or increased power consumptions?

Get the process flow diagrams and the P&ID for the plant, check the power loads in designs.

Inventory where the power is being used, include whether the power is used mechanical or thermal system

Take a good look at the top 25% of the unit power requirements and try to reduce their power loads.

Try insulation and heat loss reductions may reduce your power costs for heating.

Once you have the heat loads then look to your process production rates compared to the heat and power loads.

Check all of your mechanical drives and check the makers for power/flow and check the bearing housings for heat which may indicate poor maintenance and need for change out. Keep them cool if you can.

Do you have any steam or water discharges?? Check how much heat/steam you are losing compared to design losses.

Have fun.

Tom

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Mar 2008
Posts: 20
#8

Re: Energy Saving

04/05/2008 1:03 AM

I think it is wise to employ one Industrial engineer and look at the optimum utilization of productive resources, instead of reducing power consumption. Power consumption unless linked with production has little meaning. You will find good improvement in productivity. Apart from this the industrial engineer can also point out idle man Hrs and machinery Hrs if any. This will give you good results.

Register to Reply
Member

Join Date: Mar 2007
Location: The Netherlands
Posts: 9
#9

Re: Energy Saving

04/05/2008 5:16 AM

Depending on your compressor size, you could start with your compressed air system. Proper leak management and proper sizing of your equipment (and the control system) can result in dramatic savings, in some cases up to 50%.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2008
Posts: 19
#10

Re: Energy Saving

04/05/2008 6:26 AM

First, I would like to encourage participants to use international numbering rather than or together with local numbering, I had to look for Lakhs meaning. I suggest investing in your own power generating plant, a combined cycle (CHP). you will save a minimum of 70% of current charges, investment can be covered in 3-4 years. Afterwards, savings are completely yours. Other solutions are feasible and proven for office building and similar applications.

Register to Reply
Power-User

Join Date: May 2007
Posts: 101
#11

Re: Energy Saving

04/05/2008 7:50 AM

A few suggestions:

1. Do a plant walkthrough and eliminate steam leaks. Steam leaks mostly occurs at valves and steam traps.

2. Apply Pinch Technology to see whether you can recover wasted energy or apply energy integration.

3. For batch processes, eliminate idle time during each process step.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#15

Re: Energy Saving

04/07/2008 5:55 PM

Compressed air systems replace with variable speed screw type and drop pressure to minimum need to run all equipment. The Variable screw compressor will produce air on demand instead of cycling between high and low setting. With that you will be able to drop the pressure setting.

You will save energy in that the motor only turns fast enough to maintain air for demand and lower pressure it does not labor as much to do it.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Anonymous Poster
#16

Re: Energy Saving

04/08/2008 9:23 AM

Waste heat recovery.

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#17

Re: Energy Saving

04/10/2008 1:08 AM

Rs.1.0 lac/month is no plant at all compared to an average cost of a small chemical plant between Rs. 25.0 lac/month to 100 lacs+/month

Anyway, saving is saving big/small plant.

You've not detailed your process and media: steam/thermo oil used.

Electrical - you can go into replacing conventional motors with energy efficiency ones and replacing plant lightinging systems with energy efficient lights.

Major savings will be at steam - more efficient lesser boiler operating time lesser plant operating time hence indirectly lesser electricity.

If you have boilers try: insulating all valves & exposed pipes, stop steam leakages, install engineered steam traps on chemical reactors/vessels, return all condensate to boiler house, install boiler economizer, tune boiler burners. All these will save you 15% to 40% on your fuel bills ensuring faster production & lesser boiler operation time/plant.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bob c (3); ctwiliams (1); danuguri (1); ducon (1); DVader1000 (1); melshamy (1); ozzb (1); pascalvp (1); slong (1); Steve S. (4); Tinker65 (2)

Previous in Forum: left Hand Insertion Helicoil Set   Next in Forum: CAM Program for Hitachi Laser Drilling Machine on PCB

Advertisement