CABLE JOINTS & TERMINATION

04/07/2008 3:07 AM

Lets now be more specific:

Need step by step procedure of cable termination.

Heat shrinkable indoor termination 17.5kv, 3 x 300mm sq mm AL conductor cable XLPE, With wire screen and tape armoured with right angle boot.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: CABLE JOINTS & TERMINATION

04/07/2008 9:07 AM

The step by step procedure will be included with the termination. Otherwise check the manufacturer's website for those instructions.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#2

Re: CABLE JOINTS & TERMINATION

04/07/2008 10:16 AM

The cable jointing is a job of skill and should be done only by a competent and trained cable jointer. How ever I can give you some guide lines.

1) You must ensure that the kit is suitable to your voltage and size of the cable.Manufacturers provide these details with the jointing kit.

2) The manufacturers provide a check list of the items which you must verify before starting the job.

3) Must use a sharp knife ( special cable jointer's knife is available),LPG gas torch.and proper cleaning cloths and solvents.

4) The outer sheath , armour, inner sheath,should be cut exactly as per the dimension as per the instruction given with th kit. Manufacturers specify that.

5) You should use only the solvent supplied with the kit for cleaning.

6) Adjust the torch to obtain a soft blue flame with yellow tip.

7) The stress control tubing should not be cut.

These are only some important precautions.You should entrust the job only to an expert or manufacturers jointer as a bad termination will be a cause of breakkdown. .

Register to Reply
Participant

Join Date: Apr 2008
Location: saudia arabia, riyadh
Posts: 1
#3

Re: CABLE JOINTS & TERMINATION

04/13/2008 4:50 PM

you can call me on 0503197355 , that i am working in s.e.c

Register to Reply