Long Cable Runs and Voltage Drop

06/28/2006 9:40 AM

Roman writes:
If I run cable of about 650 meters away from my generator, using 4 core copper cable and 70 mil each core and with 400 volts, 50 hz supply of power with approximately total load schedule of 150 amps, in related with voltage drop, do you think this will have problem? Or will be have more than 5% voltage drop from point to point?

__________________
Off to take on other challenges. Good luck everybody! See you around the Interwebs.
Register to Reply
Pathfinder Tags: cables Voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#1

Long cable runs and voltage drop

06/29/2006 5:35 AM

Your cable manufacturer should have published data which will help you solve the problem. If your manufacturer doesn't (this would be a worry) then try contacting Olex cables or Pirelli Ericson. The older versions of AS3000 were a brilliant source of this data and almost anything else to do with installation. I can't remember which year they gutted it, but now we use the above mentioned books. If you can't get anything to help yourself with sing out and I'll look it up when I can. The important other thing to remember you need to identify the type of cable accurately as some cables such as Siemens have better ratings, due to stranding etc.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re:Long cable runs and voltage drop

06/29/2006 8:04 AM

I think you should do a re-calc, By canadian standard it should be 300MCM-350MCM I have a voltage drop calc excel sheet that could help you, you just punch in the data and it will give you the percent voltage drop. I would add it here if I knew how!!!

Register to Reply
Associate

Join Date: Nov 2005
Posts: 26
#3

Re: Long Cable Runs and Voltage Drop

06/29/2006 8:26 AM

From your description, it sounds like this is a three phase system, and you can tolerate a 5% voltage drop in each leg. Given that, it comes down to Ohm's Law and wire tables. 5% of the 400V is 20V, and at 150A, this gives a per-leg resistance of 0.1333333 Ohms. For a 650 meter distance, this would require a wire with a resistance of 0.205 ohms per 1000 meters. AWG wire size 000 (3/0) with a diameter of 0.41 inches (10.4 mm) has a resistance of 0.203 Ohms / 1000 meters. If you need to keep the losses lower than 20V per leg, 4/0 wire (0.46 inches, 11.7 mm, 0.16 Ohms / km) would give you about 15.7V per leg drop at 150A.

Register to Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#4
In reply to #3

Re: Long Cable Runs and Voltage Drop

06/30/2006 4:16 AM

From BS7671 your volt drop using 70mm cable is 58 volts. If you uprate to 300mm you will still have a 18 volt drop. Change to 2 off 120mm per phase will give you an 18 volt drop at a cheaper price. Is the cable in one piece, if not you will also have to make allowance for the voltage drop across the joints.

__________________
A day without a smile is a day lost
Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Emjay4119 (1); MadHatter (1); peterd (1)

Previous in Forum: Can CRTs be converted to solar energy converters?   Next in Forum: Momentary Electrical Spikes
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement