Momentary Electrical Spikes

06/28/2006 10:16 AM

Anonymous Coward writes:
Recently the Utility Company in our area experienced a major malfunction of one of their Substation Transformers. This caused a momentary spike in the distribution down the line. According to the Utility Company, the system switched over to the backup system, and the distribution down stream should not have been affected. But our place experienced a unique situation - all our secondary Breakers (600 A) tripped, but the Main Breaker in our substation did not trip. How can I prevent this from happening again? Will installing Surge Suppressors resolve this issue, or maybe a simple recalibration. Any suggestions. Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Sep 2005
Posts: 39
#1

Electrical Spikes

06/28/2006 10:25 PM

What is your incoming voltage.?? 415V, 3.3KV, 33KV or 132KV???

Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#2

Momentary Electrical Spikes

06/29/2006 5:24 AM

Both Discrimination and co-ordination are big and complex issues. Companies such as ABB, Sprecher and Schuh or Schnieder have a lot of expertise that should help you.

Reply
Power-User

Join Date: Nov 2005
Posts: 173
Good Answers: 3
#3

Tripping Breakers

06/30/2006 8:41 AM

Your secondary breakers are rated at a certain KVA in-rush on the power ladder. There are engineering safety designs configured into the power ladder design for releasing the latch in-case of overload. It is good your system did trip out as it did. I would rather have a secondary main stop the in-rush before it takes out real critical equipment. Yes you can put in a simple surge suppressant on all your critical equipemnet, how ever it does get pricey. I would reccomend not just installing a single suppressor, but to have them at the disconnect of the individual critical equipement. I would rather have each piece protected and not have the system completly down due to an in-rush. That is why certain types of breakers are installed and are designed into the power grid system of your particular structure.

Reply
Active Contributor

Join Date: May 2005
Posts: 23
#4

Surge Protection

07/12/2006 10:25 AM

I have delt with a company in Lake Park Fl called Meter treater 561-845 2007. They are experts in surge protection and may be able to help you analyse your problem.

__________________
Phil's playing golf this morning, but will be napping later
Reply
Anonymous Poster
#5

Momentary electrical spikes

08/07/2006 1:47 PM

You have to find out which relays operated to trip the secondary breakers. This could be either the undervoltage, overvoltage, earth fault, differential or reverse power relays. Once the relay is determined, add a time delay of about .05s to this relay before it trips the circuit breaker. The system should stay stable during transient power surges.

Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Emjay4119 (1); LordMaximo (1); Philp (1); Simon (1)

Previous in Forum: Long Cable Runs and Voltage Drop   Next in Forum: Termination MV Transformer
You might be interested in: Electrical Utility Services, Utility Meters

Advertisement