Previous in Forum: STATCOM   Next in Forum: Need help replacing a standard incandescent bulb with an LED bulb
Location: Home of the Hokies, Beautiful South West Virginia
Diesel Engine-Generator's (DEG) intermittent problem..
04/10/2008 9:34 AM
A diesel engine (John Deere JD3029) is a prime mover of a Marathon Electric alternator (model #284PSL1508) that supplies a power source of 208VAC, 3 phases, 60Hz, 35kW.
The problem on hand is that most of the time the DEG starts up and takes the loads fine but it fails to take any load at all intermittently. The engine will shut down due to undervoltage for some instances and due to underfrequency for some other instances.. Then, it goes back starting normally after a few failed attempts.
Is there any clue that I can go to look at to solve this annoying intermittent fails?
Computer Engineers try to solve yesterday problems with today computers. Scientists try to solve today problems with whatever tools they get hold of..
Pathfinder Tags: Diesel Engine Generator
Re: Diesel Engine-Generator's (DEG) intermittent problem..
04/10/2008 10:37 AM
The problem is more than likely in the governor, which controls the fuel. You can start by checking the speed sensors that send signal to governor.. Remove the sensors and check for damage or debris.
Next confirm your actuator (the device that controls the fuel to generator) is not sticking..
04/10/2008 10:55 AM
Does the set start on Load .If so what type of loads?
United States - Member - Northen Member Engineering Fields - Control Engineering - New Member Engineering Fields - Power Engineering - New Member
04/10/2008 11:16 PM
All good advice,
I had a 320 KW Cat machine that would not hold load of load up to rated output.
After some trouble shooting and monitoring, we found that the fuel filter housing had been machined incorrectly at the factory. A major fuel restriction was the result of this.
With this defect the machine would start and run fine under small loads, but give it a big ( 75Kw) load increase and it would slow down to the point of underfreq. Reset everything and it would restart and run again under a reduced load.
After replacing the fuel filter housing the machine would pull right up to full rated power.
It sound like a fuel delivery problem to me.
04/11/2008 8:51 AM
One possible explanation for the problem you are experiencing may be found in the drive end of the Marathon generator. This equipment can not produce electricity without first having a small electrical current being applied to the windings. This is accomplished by the use of an "exciter" mounted in the end of the unit. In that exciter there is a small diode that may have failed or is about to fail. This diode provides the "excitation" required for the generator to produce the electrical current. It is quite easy to replace and may be the solution you seek.
All that is necessary for the triumph of evil is for good men to do nothing. - Edmund Burke