4-20mA Output / Input PLC to PLC

04/17/2008 7:00 AM

We have recived a remote monintoring station to control and monitor water flow from the site , but in there wisdom there are no communication points within there package. As i am required to interface with the package, the proposeal is to provide a 4-20mA output and receive a 4-20mA Input back from the package. This in turn causes concern with interfacing between PLC's, can anybody enlighten me with a way forward with a isolating device for this porpose.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: 4-20mA Output / Input PLC to PLC

04/17/2008 8:13 AM

How far away is the station from your PLC?

If the distance is less than a kilometer, you can, theoretically, just lay out your shielded instrumentation cable and interface the station and PLC directly through isolation modules. If the distance is more than a kilometer, you'll need a repeater somewhere in between them.

Alternatively, you can go wireless. B&B Electronics has some products along these lines.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Piping Design Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Technical Fields - Technical Writing - New Member

Join Date: Jun 2007
Location: Windsor UK
Posts: 103
Good Answers: 1
#2

Re: 4-20mA Output / Input PLC to PLC

04/18/2008 4:31 AM

I'm not sure I understand your question correctly, but if you want to convert your 4-20mA signal to something friendlier for the PLC, simply connect the signal to a shunt resistor, say 500Ω, to convert to a 2-10V signal.

__________________
Those who believe in telekinetics, raise my hand - Kurt Vonnegut
Register to Reply
Commentator
Fans of Old Computers - Commodore 64 - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Control Engineering - Process Control Engineer

Join Date: Dec 2007
Location: Idaho, USA
Posts: 79
Good Answers: 2
#3

Re: 4-20mA Output / Input PLC to PLC

04/19/2008 1:43 AM

You probably already know this, but it is important that you ground your communication wire's shield at one end, but not both ends. Weird things will happen.

Here is an example of a loop isolater. There are other varieties, but this one provides true isolation. You shouldn't have any problems finding a vendor on Globalspec.

__________________
It is impossible to defeat a fool in an argument, he wil bring you down to his level and beat you with experience.
Register to Reply
Participant

Join Date: Apr 2008
Posts: 2
#4
In reply to #3

Re: 4-20mA Output / Input PLC to PLC

04/21/2008 10:03 AM

Thanks for the comments, just a note in respect to these

Distance is about 800m from the PLC, and yes i will be using line isolators at the remote end to interface with there equipment, in the past when using isolators i have found that they are not reliable in converting 4-20 to 4-20 (Passive) in a true sense, can anybody help with a reliable manufacturer for these isolator's. In the passed Ive used murr with poor results.

Register to Reply
Commentator
Fans of Old Computers - Commodore 64 - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Control Engineering - Process Control Engineer

Join Date: Dec 2007
Location: Idaho, USA
Posts: 79
Good Answers: 2
#5
In reply to #4

Re: 4-20mA Output / Input PLC to PLC

04/21/2008 7:54 PM

There is an interesting solution out there where you can convert the 4-20mA signal to a fiber optic one and then back again to 4-20mA on the receiver end.

http://weedinstrument.com/product_groups/fiber/analog_system.html

These are not real common but the datasheet said they have 0.1% accuracy. I have not used them before, but they caught my interest and I thought of your application.

__________________
It is impossible to defeat a fool in an argument, he wil bring you down to his level and beat you with experience.