Standard Test Value for MV Power cables

04/18/2008 11:03 AM

Dear All

Could you told me what is the standard test for MV (20KV) power cables ? what is the minimum value that still accept to operation such as :

- Insulation resistance

- Hi Pot

- Partial Discharge

- Dissipation Power Factor Tangent Delta

Thank you for your help

Regards

Siswanto

Email : sis_cahya@yahoo.com

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Sep 2007
Posts: 49
Good Answers: 1
#1

Re: Standard Test Value for MV Power cables

04/20/2008 1:54 AM

Dear Friend

Which test do you mean? Type test, Sample test or Routine test? It is better for you to read IEC 60502-2 if this standard is applicable for your project.

Good luck

__________________
A thousand-mile journey begins with the first step.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: Standard Test Value for MV Power cables

04/21/2008 6:01 PM

Standard acceptance testing for new electrical equipment is:

(2E + 1,000). 2 x (equipment voltage rating) + 1,000 volts.

This is for new equipment and is not acceptable for used equipment that may have dry and/or damaged/fatigued insulation conditions. Follow the test equipment manufacturer's recomendations very closely. If you are not absolutely sure what you are doing, consult a certified test facility for their input and guidance. If you apply too high of test voltage, the equipment will fail.

Good luck

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."