Hi everyone
I am designing LV power distribution for an industrial application. 10kA max. short circuit current.
I do not know what existing loads are, however I have existing fuse ratings protecting main DB submains (basic arrangement is main switch/cb feeding 2-off DB submains). Existing arrangement is 200A fuse to each DB.
I need to design to replace 200A fuse with MCCB. However, I need to ensure discrimination between the two DB MCCBs and the main switch such that the two MCCBs available (for my chosen manufacturer) are 160A and 250A only.
The tripping curves for the 160A show that at 200A the breaker will take a minimum of 5 mins to trip.
What about the fuse? If I can argue that the fuse would likely trip before 200A (based on real data) I can justify the replacement of the 200A fuse with the 160A MCCB.
Does anyone have any thoughts on my method?
Can anyone direct me to some fuse tripping curves, I cannot find any!
Thanks everyone
MB