Diifferential relay Stability testing for transformer

04/23/2008 10:06 AM

I need a help to find out whether the method adopted was right or it may have some effects on transformer.

We have 5 MVA 11/11 delta-star transformer with % impedance 12.6.

We want to test the stability of the differential relay ABB make RADHA.

We short circuited the transfomer secondary terminals in Breaker panel

first created zonal & then out of zone fault to test the relay stability.

We had give 440V 3Phase supply to primary while secondary was short circuited.

current observed to be 160Amps.

I want to know whether this test is okey or it may affect adversly on transformer performance due to the inrush current while short circuited mode.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Diifferential relay Stability testing for transformer

04/24/2008 9:01 AM

Prassanna,

I do that all the time.

You used 440 V for the current injection but you didi not say what is the voltage rating of the transformer.

I recently used 4160v injected into a 132KV 160 MVA transformer with 12.5 5 pu impedance.

Worked fine with no possible damaged to the transformer

Register to Reply
Active Contributor

Join Date: Nov 2007
Posts: 10
#2
In reply to #1

Re: Diifferential relay Stability testing for transformer

04/29/2008 9:07 AM

Thanks for your reply,

Transformer rating 5 MVA 11KV/11KV Generator isolation Transformer