Copper Busbar Sizing

04/27/2008 11:38 AM

sir

for 2500A ACB we had used 80mmx10mm x 2 + 80mmx5mmx1run Copper Busbar for Each Phase ,is it ok ? we had consider 1.3A /Sqmm Current Density for this case

I just want to Kmow Because of this Uneven busbar Sizes any problemof Heating or Skinning is occurs or not ?or selection is wrong

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: Copper Busbar Sizing

04/27/2008 11:34 PM

Welcome Santosh,

I will not recommend a mix of sizes.

80 mm X 10 mm X 2 bars is enough (for even 3200 amps at 45 deg C ambient).

Cheers.