How to select Capacitor Bank for Electrical Panel.

04/28/2008 3:53 AM

Respected Sir,

We Have Paint Shop, Injection Molding Machine, Compressors( Near About 450 Kw Load ) We install automatic power factor Controller for bank. Total banks 280 KVAR but from some days all banks getting on & power factor also not improving we check also all banks its found ok.

So we decided to installed fixed bank to paint shop electrical panel, but i have doesn't know how select capacitor bank. So Plz guide me

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: How to select Capacitor Bank for Electrical Panel.

04/28/2008 9:22 AM

The automatic power factor corrector unit ( APFC ) operate from the input from CT and if there is no load current, the control system operation will be in effective. But the actual pf will be low due to transformer inductance . So it is better to maintain some fixed capacitor in addition to the APFC .

The calculation of capacitor KVAR Will depend on the present and required pf .

In case your present pf is 0.7 ( Cos Φ1) and if you want to improve it

to 0.95 (Cos Φ2) the normal equation followed is :-

The kVAR = kW ( tan Φ1 - tan Φ2 )

The kVAR may be added and switched off in steps on both automatic and manual switching. You should check the PF meter also. It may not be operating properly.

Register to Reply
Commentator

Join Date: Aug 2007
Location: INDIA
Posts: 58
#2
In reply to #1

Re: How to select Capacitor Bank for Electrical Panel.

04/28/2008 11:46 PM

Respected Sir,

Thank You for great reply, But till i have some queries if u send me Ur mail id / mobile no than i can contact you. I am also staying in pune & working in Minda Valeo Company.

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#3

Re: How to select Capacitor Bank for Electrical Panel.

04/29/2008 9:47 AM

Before adding more capacitance, look at the problem. I am surprise that 280 KVARS is not enough to compensate a 450KW load and improve the power factor. Can you give us numbers? We need to know the PF, the power... This band should be plenty even if you have many induction motors. The only loads that could demand such a high correction are welding machines and large DC motor drives. If you don't have much of those, you will not fix the real cause of your problem.

First is is OK to have a low power factor at low load. It doesn't cause any problem. If your utility is giving you a penalty, tell them to use a minimum threshold of the power factor meter or simply use the peak KVARs instead of the PF. This is a better measurement anyway. The PF is simply a ratio and doesn't mean much at low load.

Make sure that the PF meter you are reading is placed upstream of the capacitor bank to see its effect. Make sure that the controller is operating properly. Do you measure current in the capacitor banks?

Don't look for PF=1. Expect 0.9 to 0.95 as being good values. Also, if you over compensate your power factor will decrease in the leading direction. This could be your problem. Check the sign on your PF meter.

Finally, remember that too much capacitance can cause resonance problems that can be destructive for the plant sensitive equipment.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: How to select Capacitor Bank for Electrical Panel.

05/31/2009 10:16 AM

hai i am kannan, in my experiance you can go about 180 KVAR

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5
In reply to #4

Re: How to select Capacitor Bank for Electrical Panel.

05/31/2009 11:13 AM

Kannan

Would show you calculations how you came up with 180 kvar. You do not know the present power factor so how can you make this statement? Please describe you method.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers: