690 Voltage Transformer

04/28/2008 7:23 AM

i am working in power plant and i installed 11kv / 720volt transformer.transformner have two secondary winding each have 720 voltoutput.one winding is star connected and another is delta connected.power from both secondary fed to VFD panel .iwant to known why 720 volt is used in place of general LT voltage 440 volt.also what is advantage of dual secondary windings.

regards

suresh kumar paliwal

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#1

Re: 690 Voltage Transformer

04/29/2008 5:42 AM

If one secondary winding is star connected and the other delta connected, then there is a phase shift of 30 electrical degrees between them.

If you are going to rectifier this AC signal into a DC signal, you have a much smooter DC current. You can use a 12 points rectifier. The following capacitor to store the energie can be much smaller.

Why 720 Volts in stead op 440V ? Probably because in this case you can hold the relation between volts and herts constant over a bigger range.

A motor designed for 440V 60Hz can be operated at 98 Hz, without lossing shaft torque. If the motor is connected in 440V delta and supplied with 720V 98Hz.

So you can take much more mechanical power out of your motor.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#2
In reply to #1

Re: 690 Voltage Transformer

04/29/2008 9:58 AM

"Why 720 Volts in stead op 440V ? Probably because in this case you can hold the relation between volts and Hertz constant over a bigger range."

Well, maybe in the books but in reality, higher voltages are used in the industry to save on the wire size. The higher the KW of the load, the higher the voltage used. This usually works by class in order to standardize the equipments.

Most plant will use 600V in Canada for the 50KW to 1MW. Above this we will use 4160V. Below this we use 120/208V.

In the case of a power plant, they often use 690V simply because they have standardize on this and most equipment used in this industry is made for this. 720V is not very far from 690V and can probably be used on the same feeder simply by adjusting the transformer taps.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.