12 puls invertor in VFD

04/28/2008 7:25 AM

waht is diffrence in 6 pulse and 12 pulse invertor of VFD .waht is exact criteria of use of 12 pulse and 6 pulse invertor .

regards

paliwal

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: 12 puls invertor in VFD

04/29/2008 2:08 AM

A 3 phase full wave bridge rectifier has 6 diodes, hence the name "6 pulse".

To reduce harmonics, one trick is to use two separate 6 pulse rectifiers fed from a phase shift Delta - Wye (Star) transformer. 6 + 6 = 12 pulses. The phase shift from the transformer moves more of the harmonics into the triplen and even order ranges where they cancel each other out. 18 pulse is even better.