Area Classification

04/29/2008 1:14 PM

Hello Frnds,

We have for our project Clasified for Cl1, DIV 1, Gas group C,

If I have to change for zonal classification(as per clients stds),i would assume (If I am nor wrong to be) CL1 , Zone ( ?) , Gas group II B

Now my problem is how to change Div to Zone , should i go for Zone 0 or Zone 1

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Area Classification

04/29/2008 3:51 PM

Well DIV1 is classified as "gas likely to/can exist under normal operating conditions" (which sort of matches Zone 1). Zone 0 is "continuous or long term" presence of gas (such as inside a storage tank).

I cannot really say as there will likely be other requirements due to differences in the standards (they are not completely interchangeable). One of the main differences of course is DIV1 could mean either Zone 0 or Zone 1. You will need to assess yourself (or get someone else to) if this particular site is either Zone 0 or Zone 1.

__________________
jack of all trades
Register to Reply
Anonymous Poster
#2

Re: Area Classification

04/29/2008 11:14 PM

Hello,

Check this: gmisafety.com/?p=intrinsic_safety

Regards

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#3

Re: Area Classification

04/30/2008 12:53 PM

Thanks for the Inputs

Regards

Jose

Register to Reply
Participant

Join Date: May 2008
Posts: 2
#4

Re: Area Classification

05/01/2008 7:18 AM

The last reply was INCORRECT:

Div 1 = zone 0 and zone 1 (therefore you have to pick the worste case and make it zone 0) This is confimed by the fact that you cannot install zone 1 rated equipment in a div 1 location (you need to use zone 0 equipment), BUT you can install div 1 equipment in a zone 1 location (BUT not a zone 0 location). confused yet?

Div 2 = zone 2.

Div System Zone System

Div 1-------Zone 0

-------Zone 1

Div 2-------Zone 2

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#5

Re: Area Classification

05/11/2008 7:37 PM

A second "yes" for Whycliffrussell and a link to the UL

http://www.ul.com/hazloc/gascon.pdf

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (1); josej (1); TVP45 (1); whycliffrussell (1)

Previous in Forum: PID Tunning   Next in Forum: To Control the Water Level in a Tank

Advertisement