Generator Voltage Problem

05/02/2008 3:57 PM

We are testing a three phases diesel engine generator and experiencing a problem of the increase of output voltages on each phase whenever an external load is applied. Without a load, its output voltage is well regulated at 208V phase to phase and 120V phase to neutral. However, when a load is applied, the output voltage is increased to about 138V phase to neutral and 240V phase to phase. We are wondering anyone who has experienced this before and could tell us where we should look at.

__________________
Computer Engineers try to solve yesterday problems with today computers. Scientists try to solve today problems with whatever tools they get hold of..
Register to Reply
Pathfinder Tags: Generator Voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Apr 2008
Location: south africa
Posts: 19
#1

Re: Generator Voltage Problem

05/02/2008 5:44 PM

I'm not an expert, but maybe you have an automatic voltage regulator (avr) as a controller and the avr is over responding to the electrical loading of the alternator, the avr is designed to maintain the rpm of the machine thus frequency and output voltage is kept constant.

one way of checking is to ensure that the speed is not suddenly increasing as you load up the machine.

best of luck

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#4
In reply to #1

Re: Generator Voltage Problem

05/03/2008 12:22 AM

Hello Ally,

Just a correction..Avr controls the voltage and does not control the rpm of the machine.

Check the droop setting in the AVR of the generator.

What is the Pf reading on load ?

I suggest calling the supplier tech representative to deal with this if the machine is still under warranty.

The rpm of machine is controlled by governor which is a different animal.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7
In reply to #4

Re: Generator Voltage Problem

05/03/2008 2:56 PM

Perfect answer. I gave you a GA for that.

Droop characteristic is the problem. In fact the droop is a rise for some reason!!! The AVR should then be lowering the excitation to achieve a steady and correct voltage.

It is possible to design an alternator to have a rising characteristic instead of a droop, its not usual, but completely possible.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Generator Voltage Problem

05/02/2008 7:59 PM

How much of a load are you placing on the genset when its output goes high?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Anonymous Poster
#3

Re: Generator Voltage Problem

05/02/2008 8:10 PM

If you have a no load run, what does the voltage regulator regulate (you said that it works OK) ?

Usually, the voltage regulator has a reference voltage with whom it compares the output voltage and, if the voltage is lower, it increases the excitation voltage to bring it back to the prescribed value ( with a +/- 2.5% usually). This voltage drop occurs when you apply load. How much is tends to go down depends on how much and what type of load you apply ( more for inductive load, less for resistive load and the least for capacitors (in this case you may even see an increase in the output voltage with increased load)). If the speed of the driving motor goes down (and it usually tends to go down when you apply a load to it), the speed (rpm) regulator tends to bring the speed up to the set value ( corresponding to 60 Hz). If the speed regulator does not work, the voltage regulator has to take care of this drop in voltage too and correct the difference in voltage. However it does not take care of the frequency difference (Hz). The described symptoms tend to point out to either a defective voltage regulator or a capacitive load, that the existing regulator cannot handle. Check also the frequency (it should be stable at 60 Hz)

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: Generator Voltage Problem

05/03/2008 4:51 AM

I totally agree with views expressed by the guest.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#6

Re: Generator Voltage Problem

05/03/2008 4:56 AM

Its a long time since I had anything to do with this, but an AVR should be controlled by a PID unit. Proportional, Integral and Derivative control.

Proportional responding to the difference in set point, Integral the rate that a set point is varying, Derivative the time it is away from set point.

Integral and derivative normally cause large hunting swings, so if the voltage is steady at a larger reading, then it may suggest a proportional band setting? droop I think would accept a drop before reacting?

Like I said its been a long time, others may need to fill in.

Regards JD.

Register to Reply
Anonymous Poster
#8

Re: Generator Voltage Problem

09/18/2009 4:12 PM

The problem is most likely swapped phases on voltage sensing and/or wrong current direction from CTs to load controller/AVR, as the droop on the machine is working in the opposite direction.

Register to Reply
Participant

Join Date: Jan 2013
Posts: 1
#9
In reply to #8

Re: Generator Voltage Problem

01/20/2013 8:27 PM

What if the AVR does not have a pot to adjust the droop setting.On this 20kVA leroy sommer alternator I was working on the AVR had pots for adjusting volts and stability only no droop.

What's the stability adjustment for?

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ally z (1); Andy Germany (1); Anonymous Poster (2); chaterpilar (1); Helpme (1); jdretired (1); nesubra (1); North of 60 (1)

Previous in Forum: Using NPN Encoder Output   Next in Forum: 120 volts to 220 volt conversion

Advertisement