Air Conditioner Help

05/14/2008 12:40 PM

help me please before i go to repair shops hehe, i've notice that the aircon in my bedroom gives off small amount of air when it is turned on for about 4 hours, and i notice that large chunks of ice are surrounding the radiator like metal ( i dunno what the name of that part but it looks like a radiator, it has curve metal pipings and it is located right after the filter). what do you think is the problem? or maybe the posible solution for this problem. it seems that the ice chunks are that are forming in that radiator-like part is preventing the air to go inside the aircon.

Register to Reply
Pathfinder Tags: aircon
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: AIRCONDITONER help

05/14/2008 12:50 PM

It sounds like it is working properly but has a blockage, and low airflow probably caused by plugged filter.

Clean or replace the filter

Melt all the ice of the 'radiator'. Boiling water will make short work of the ice.

Make sure any vent lever is open, and any other blockage is removed.

The other possibility is the fan is not working at the proper speed. It could be a slipping belt or the fan motor itself.

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Associate

Join Date: Feb 2008
Location: manila
Posts: 29
#2
In reply to #1

Re: AIRCONDITONER help

05/14/2008 12:52 PM

where can i find this vent lever?, btw it seems that when i clean the filter 1 week ago i have touch that metal wire that has a round like end, i think its a temp. indicator thing and also the ground wire. do you think this could be the cause of this problem?

Register to Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#3
In reply to #2

Re: AIRCONDITONER help

05/14/2008 1:00 PM

It depends on the model.

Some of the older ones had a small lever right in bottom of the grills. Others simply have adjustable grills. Others yet, have controls for recirculating inside air or using outside air.

It may not even have one.

If you damaged the thermistor It would do one of two things:

  1. the compressor would never stop producing cold air and cause icing to build up.
  2. It would never produce cold air

Make sure none of the wires going to the thermister is touching metal

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Associate

Join Date: Feb 2008
Location: manila
Posts: 29
#4
In reply to #3

Re: AIRCONDITONER help

05/14/2008 1:15 PM

maybe thats the problem hehe, thanks very much!

Register to Reply
Associate

Join Date: Apr 2008
Posts: 33
#5
In reply to #4

Re: AIRCONDITONER help

05/14/2008 10:21 PM

If you are producing ice --and haven't asked for it, it can be almost only one problem--the system doesn't register the temperature of the air leaving the heat exchanger(either the air isn't moving properly or doesn't register its temperature) it doesn't know to shut the thermal expansion valves off. It can be a restriction in air flow through cool side of the system or a bad thermocouple or both. The high side would seem to be working fine(compressor/condenser) if the system had the capacity to freeze anything.

Register to Reply
Anonymous Poster
#6

Re: Air Conditioner Help

05/14/2008 10:56 PM

remnants; check the coils that you can see from the back side of the unit you cannot believe how plugged up they can get hi pressure hot water could clean them out, perry

Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#7

Re: Air Conditioner Help

05/14/2008 11:20 PM

Another possibility- you have the thermostat set to maximum, so the unit never cycles properly, causing a buildup of ice...Try setting the thermostat about mid-range.

Register to Reply
Participant

Join Date: Apr 2008
Posts: 2
#8

Re: Air Conditioner Help

05/14/2008 11:43 PM

Sounds like you have a window AC or thru the wall.

You must give attention to the thermostat bulb.

It is not only a thermostat, but a de-icing control as well.

1. It must be mounted with the factory mounting clip in the precise place where it was from the factory.Hehe. All window a/c units will ice up if allowed to run continuously.

2. Your thermostat points may well be welded closed, so that, even though the bulb senses the ice building up,hehe, it allows the compressor to continue to run.

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#9

Re: Air Conditioner Help

05/15/2008 1:16 AM

Hello RemnanTS

The de-icing feature built into most refrigeration and air-conditioning systems works by sending a periodic pulse of hot compressed gas through the cooling coils, heating them, and driving off accumulated moisture before it has a chance to freeze to ice.

That way, ice does not ever build up.

It is possible your thermostat has failed, or stuck on max.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Associate

Join Date: Apr 2008
Posts: 33
#15
In reply to #9

Re: Air Conditioner Help

05/15/2008 11:29 PM

I think you are right--In Ammonia systems it's called hot gas bypass--Hot gas directly from the compressor is diverted to the coils and defrosts them in a huge hurry(of course, unless I am mistaken).

Register to Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#10

Re: Air Conditioner Help

05/15/2008 2:19 AM

I'm not an air conditioning specialist but it is also possible the refrigerant charge in the unit is not right.

j.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#18
In reply to #10

Re: Air Conditioner Help

05/24/2008 2:53 PM

You are right the quantum of refrigerant need to be checked and should be recharged to the correct level to solve the ice formation in the condenser pipes and to improve the cooling power of the AC.

Register to Reply
Associate

Join Date: Jan 2008
Location: USA
Posts: 38
Good Answers: 2
#11

Re: Air Conditioner Help

05/15/2008 8:45 AM

You could have thermostat problems as several have indicated.

You could be low on refrigerant. An interesting thing happens to home air conditioners when they are low on refrigerant.

When properly charged, refrigerant liquid and vapor flow through the evaporator coil (the part that looks like a radiator where the ice builds up) at roughly 45-55 degrees F until all the refrigerant evaporates. Then the vapor superheats to a few degrees below ambient temperature before re-entering the compressor.

When the refrigerant charge is low it works a little differently. Where liquid enters the evaporator coil , the pressure is too low and it gets too cold right right where it enters. There is actually less refrigerant flowing, so all the refrigerant quickly evaporates and begins to superheat. Only a small portion of the evaporator coil is working and it is too cold.

Since it's too cold where the refrigerant initially evaporates, it freezes moisture out of the air. After the air flow stops through the blocked part of the evaporator, there is relatively little load on that part of the evaporator and the frozen zone advances, eventually freezing the entire coil.

If you observe the freezing zone advancing from where the refrigerant enters the coil to where it leaves, this is probably the cause. You have a leak somewhere in the refrigerant loop and the charge is low. Find and repair the leak, then recharge properly, and you're back in business.

__________________
All generalizations are false, including this one.
Register to Reply Score 1 for Good Answer
Member

Join Date: May 2008
Posts: 6
#12

Re: Air Conditioner Help

05/15/2008 11:09 AM

It looks like you have to check deferent issue at your AC system and fixed to prevent damaging the compressor Through my experience when the ice build up on the evaporator coil (radiator) that strongly indicated long cycling system, that cause by low set point for the thermostat or the AC condenser under charge ( low refrigerant).

Well, I recommend you to do this:

- let the ice milt by shut down the unit for 48 hours.

-check the condensation drain and clean it up.

-replace the Air filter (if it is replacement) or clean it up if it washable.

- check for the evaporator coil (Radiator) and clean it up carefully by using low pressure air

- adjust the supply air registers in the house to make sure the deliver equal air to the rooms.

- turn on the system, and wait 10-15 minutes then check the supply air temperature on the closest register to the evaporator coil. it should below 60 f degree. if not. you have to check the refigerant charge for the system probably under charge, unit has leak. or it has restriction.

Register to Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#13

Re: Air Conditioner Help

05/15/2008 6:34 PM

You are low on refrigerant.

Register to Reply
Member

Join Date: May 2008
Posts: 6
#14
In reply to #13

Re: Air Conditioner Help

05/15/2008 11:02 PM

And your filter plugged up.

Register to Reply Score 1 for Off Topic
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#16

Re: Air Conditioner Help

05/15/2008 11:29 PM

Hi RemnanTS,

Since you are getting ice, the AC is cooling fine. What is not working is the part that gets rid of the heat. That part is outside the house. Either the outer fan is not working or the fins are plugged up with dirt. There are other possibilities that will take a professional to find. Good luck.

regards,

S

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Commentator

Join Date: Mar 2008
Location: Strongsville, Ohio USA
Posts: 62
#17

Re: Air Conditioner Help

05/19/2008 8:18 PM

It's just a window shaker men. No hg bypass on those toys. ( throw away pieces of #@*&). Dirty evap coil or oa ambient lower than 68 dg f at night while he runs it all night.

Register to Reply
Register to Reply 18 comments

"Almost" Good Answers: