CABLE SIZING

05/19/2008 4:00 AM

WHAT IS MAX CABLE SIZE CAN BE USED FOR 20mA, IF THE INPUT VOLTAGE IS 24VDC.

q2 : HOW THE VOLTAGE DROPE CAN BE CALCULTE FOR INSTRUMENT CABLE

q3: WHAT THE RELETION BETWEEN DISTANCE AND RESISTANCE IN CABLE SIZING

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#1

Re: CABLE SIZING

05/19/2008 5:27 AM

For maximum cable size for a 4-20mA signal, I wouldn't use much bigger than a 2AWG.... because anything bigger would be really silly. As for what I suspect you are wanting is Minimum size... I'm not really sure. I usually just use 16-18AWG for my 4-20mA signals because it is the most convenient size. As for the rest, it sounds like you are asking homework questions, and I don't know the answers off the top of my head, so do what I would do and ask Google.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: CABLE SIZING

05/19/2008 7:54 AM

A0) Please turn off caps lock. Capitals use IS CONSIDERED SHOUTING AND RUDE.

A1) 0.75mm2 is a typical size used in industry in the UK. It is based upon the mechanical robustness of the conductors more than anything else. Any bigger and it won't go in the terminals on many commercially-available instruments.

A2) For a 4-20mA current loop, it really doesn't matter much unless the cable length starts getting up into the >1km region, after which it needs to be considered though the effect will sometimes be small; 20mA into 100Ω is only 2V, after all. There are a number of techniques used to overcome excessive loop resistance, including current repeaters, fibre-optic transmission and voltage sensing and boosting circuits.

A3) Almost linear.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#3

Re: CABLE SIZING

05/21/2008 3:27 AM

The total resistance of the loop shall be less than 1200 Ohms, including the impedance of the generator...