I have a large motor starter which uses CTs to feed to the over load relay, and the OLR is tripping prematurely. In fact I can see that there is NO over load with my clamp-on CT, yet the OLR is tripping anyway.
One of the CTs is installed so that the polarity mark is opposite of the other two. Could this have an effect on the operation of the OLR? It is a solid state OLR which, I believe, has sensitivity to current imbalances. I am of the opinion that the one CT being installed backwards will make that phase current the opposite polarity of the other two, so it will appear as a current imbalance. Does this make sense? Others in my team say that CT polarity makes no difference in anything other than kW metering.