Current Capacity for Vacuum Circuit Breaker

08/04/2006 11:26 AM

ANIL KUMAR writes:
I request your advice in selecting current capacity of vacuum circuit breaker/contactor for running 4 no. 3.3kv AC Induction motors ,750 kw drawing 145 amp at full load.We want to have one no. incoming panel and four no. out going panels.Kindly provide calculation for the same.
Anil Kumar
Superintending Engineer,
U.P.Irrigation Dept

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Aug 2006
Posts: 1
#1

What is your system?

08/05/2006 1:40 PM

What is incoming panel and four no. out going panels? What do you mean? How many starts per hour will you have? What type rotors have AC motors got, short-circuited rotors or phase-wound rotors? What type a torque do you have? How offen will you turn off motors in start time? How long must work your system without service?

Reply
Active Contributor

Join Date: Aug 2007
Location: HCMC, VietNam
Posts: 16
#2

Re: Current Capacity for Vacuum Circuit Breaker

08/20/2007 3:16 AM

Select circuit breaker/contactor for motor load, we must to know something:

  • Votlage 220V/380V/415V.
  • D.O.L starting or start-delta starting.

DOL Full load curent starting 6xf.l.c and max 5secs starting time.

Star-delta starting full load current 2xf.l.c and max 15secs starting time.

For more information you can see according to IEC 60947-4-1.