Generator Excitation

06/02/2008 1:34 AM

We have a 5 MW Gas Turbine Generator (Turbine of Solar & Generator of Katto).

Recently we have overhauled the generator by local Veendor as well as carried out Turbine Rotor machining by solar.

The observations found regarding the Excitation requirement are as follows.

Before any work,

No load Excitation 18 V

Full Load Excitation requiremnt 36V

After the said work,

No load Excitation 35 V

Full Load Excitation requiremnt 85V

Though the nameplate of exciter shows 100V, 4A

What must be gone wrong to have so much variation in excitation requirement?

Please help me out.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#1

Re: Generator Excitation

06/02/2008 9:33 AM

What is your excitation current?

Register to Reply
Active Contributor

Join Date: Nov 2007
Posts: 10
#5
In reply to #1

Re: Generator Excitation

06/03/2008 9:39 AM

The rating of exciter is 100V, 4A.

It is showing 3.4A at 80V

I.e. it is in linear zone only.

Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#2

Re: Generator Excitation

06/02/2008 11:36 PM

Contact Mr.satish Rao at Katto he would be of help

crm

__________________
Run silent run deep
Register to Reply
Active Contributor

Join Date: Sep 2007
Posts: 21
#3
In reply to #2

Re: Generator Excitation

06/03/2008 3:19 AM

yes, contact the equipment manufacturer/ vendor.

Register to Reply
Active Contributor

Join Date: Nov 2007
Posts: 10
#4
In reply to #2

Re: Generator Excitation

06/03/2008 9:37 AM

Thanks for reply.

Do you have his contact no?

Register to Reply
Anonymous Poster
#7
In reply to #2

Re: Generator Excitation

06/08/2008 10:57 AM

if u hav, please pass on no. of Mr. Satish Rao of Katto,

Thanks

Register to Reply
Anonymous Poster
#6

Re: Generator Excitation

06/03/2008 12:21 PM

since the rating is 100 v ,4A . present condition is ok. propably the meter connection conection may got changed. please check the multiplication factor of the meter. ponnusamy thanjavur , india