Previous in Forum: power cord-plug   Next in Forum: Fail Lamp Detection.
On load tap changer
06/03/2008 3:46 AM
I am a professional repairing more than 32 models of OLTCs made by various manufacturer eg MR, Elin, Trafo Union, ATL, Fuller, etc. Any one having problem with on load tap changers may please contact me.
I am in this field for 32 years.
Pathfinder Tags: oltc
Re: On load tap changer
06/03/2008 6:59 AM
Dear vs rathore
Please let me know your comments on connecting two HV transformers in parallel with different Tap settings. Is there any standard limit (IEEE or IEC) for the circulating current.
Thank you
Dr. Gaouda
06/12/2008 7:32 AM
Hi,
If two transformer are in parallel then the taps shall also be in the same position. An AVR shall be provided in the Transformer RTCC panel.
N.Suresh
01/26/2009 12:43 AM
When paralleling two transformers it is advisable (among other factors) that they should have the same tapchanger, otherwise circulating currents will be produce. Industry standard set this at 10% maximum.
Having the same characteristics and tapchanger brand, two transformers operated in parallel will not always be able to synchronize their voltages. This is because no two tapchangers even of the same brand and type will ever behave in the same way. That is why, the circulating current can not be totally eliminated but can only be mitigated.
In practice, we have paralleled power transformers several kilometers apart for a few hours without undesirable effects.
08/12/2009 12:42 AM
We are going to attempt to parallel 2x 30MVA transformers (1x 132kV, 22 step OLTC & 1x 138kV, 33 step OLTC) using Beckwith's M2001B "DeltaVAr 2" method.
Has anyone else been successful in getting this system to function properly?
Thank you.
GMK, P.S.E.
06/13/2008 1:56 AM
Dear Dr.,
I was busy with Merilli make tap changer repair.
Please note that transformer once paralled meeting all the condition of parallel operations, can make on load tap change with one step out in amongst them.
The OLTC controls block any further operations.
Transition resistance thermal with stand capability and Resisitor contact breaking capacity limits the amount of current handling capability. Load current plus/ minus circulating current all that matters during transition.
IEC 214 please may be refereeed to.
Regards,
VS Rathore
10/15/2009 9:56 AM
we have two oltc Mitsuhishi catalogo 1B-67047-C, we need change resistence and contact failure, were need found this parts?, these below to 2 tranformer 20 mva 115-13.8 kv, can you help us
thank you Henry / Venezuela
07/02/2014 7:49 AM
Dear Mr Rathore,
Its great to learn about your experience. We have a case where the existing 25 MVA transformer with 5 no of off-circuit taps positions. This needs to be retrofitted with OLTC having atleast > 11 steps sinoltage. Please suggestce we have frequent variations in I/C v
Register to Reply 7 comments