Hi
I need to pick somebody's grey matter on the following issue with regards to a fail lamp detection circuit.
The Supply voltage for the lamp is 24v dc. and what is needed is a circuit that would tell the operator in the control room that the lamp is functional or not via and audible or visual display. The current system which uses relay works. But i am trying to figure out the logic on how it works..
First the dc supply goes directly to the lamp and in series with the cirucit is a small 6V DC relay. The contacts of the relay is then used as a signal to indicate whether the lamp is working or not. Wired in parallel across the relay coil is a 120 ohm,10W relay.
Why do u need a 120 ohm resistor across the relay coil?
In another instant, there is a 12vDC relay connected in series with a 2.2 ohm ,10w connected across the relay. This circuit is also is to detect the falure status of the 24v lamp.
Can anyone help please..
"Shallow men believe in luck. Strong men believe in cause and effect." -- Ralph Waldo Emerson
Re: Fail lamp detection.
06/03/2008 7:18 AM
Seems horribly overcomplicated...
A simple non latching push button to connect the 24v DC to the lamp to test it would surely suffice?
If you add more 'stuff' you add to test circuits, then you end up needing test circuit test circuits... so on ad infinitum
06/03/2008 7:30 AM
Del...with due regard to your concern, the query is to annunciate the failed lamp to a remote location.
A lamp test (button) is an option which you find in most panels..but the OP wants to know how to annunciate it to a remote control panel without pressing the lamp test button.
Cheers.
He must be very ignorant as he answers all the questions he is asked. Voltaire
06/03/2008 7:36 AM
Ah if only the poster was as lucid as you my orange striding friend....
Good Answers: 266
06/03/2008 7:45 AM
The 120Ω resistor is to hold a sable voltage drop across the coil of the relay. In series with the lamp the coil is being held energized while the lamp is on. Contacts open to the alarm. If the lamp blows creates an open circuit. Alarm relay closes alarm goes off.
06/03/2008 7:59 AM
Hi Ozzb and all..
Thanks for your explanation. In fact i am also wondering,why in two cases, the original circuit uses a 6V relay in one instant and a 12v in another instant to sense the lamp failure.?
How would one calculate that the value of the resistor should be 120 ohm? I know it cannot be very high because the lamp would lose its brightness intensity. The power of the lamp is 45W , 24V.
Joy to u and shalom
06/03/2008 8:05 AM
They probably used what was easilly available, or a 'standard' part from their stores...the resistor values were probably selected simply to 'make it work' rather than as a result of some feindishly clever calculation.
06/03/2008 11:16 AM
OK. Now for some sums:
(24V)2 / 45W = 12.8 Ω filament resistance at this voltage.
Dropping 6V across the resistor, and making unrealistically no allowance for the variation of lamp resistance with applied voltage, nor the resistance of the cable
18V / 12.8Ω = 1.41A drawn by the lamp with this relay in series with it.
Relay + resistor in parallel: 6V / 1.41A = 4.3Ω
Resistor draws 6V / 120Ω = 0.05A
Therefore relay is drawing 1.41A - 0.05A = 1.36A and has a resistance of 6V / 1.36A = 4.4Ω, more or less.
Therefore Del's suggestion that the installer just happened to use a resistor that was hanging around is probably correct, and it is more than likely now that it is there as a voltage spike eliminator than anything else. The selection has probably been made on a practicality and safety basis rather than anything more esoteric.
Note that a silicon rectifier, like the 1N4001 (cheap as chips), could have been used instead of the resistor provided the rectifier was arranged reverse-biased; this is a common way of preventing high voltage spikes appearing at relay terminals on DC circuits.
06/03/2008 8:06 AM
<...Why...a 120 ohm resistor across the relay coil?...>
It's there to provide enough current to light the lamp while simultaneously dropping enough voltage to energise the relay while the filament is intact. The lamp might be "under running" as regards its rated voltage, which extends its life considerably, or it might be an 18V lamp, perhaps, in series with the relay coil.
As a secondary feature, wiring a resistor across the relay coil prevents a high reverse voltage being generated at the relay terminals when the field collapses, as would happen when the upstream switching circuit turns the lamp off, when the filament breaks, or maybe while a technician is handling the lamp during a replacement operation with the circuit live.
Sometimes a critical lamp can be supplied with dual filaments. When the main filament breaks a relay changes it onto the reserve filament and annunciates the failure remotely for the purposes of lamp replacement, which is common practice in railway signalling equipment; the integrity of these lamp filaments is critical to giving the correct signal aspects to the driver of a train, particularly when it is to display colours other than green.
There is a possibility, with LEDs replacing filament lamps in many industrial control panel applications, that lamp integrity circuits and lamp-test pushbuttons will become a thing of the past.
06/03/2008 11:37 AM
Ooooooh! More! More!
If the filament of a signalling lamp is detected in this way, the fracture of a filament, which causes the detector relay to change state, can also be used to change the aspect of a signal to one that is more restrictive (being an important consideration in railway safety). For a green/double-yellow/single-yellow/red 4-aspect colour light, for example:
  • If the green filament breaks the signal in rear can be wired to show double-yellow at best, as well as the signal in question.
  • If one of the yellow filaments breaks the signal itself will show single yellow, no problem, and the detector circuit can be made to override the signal in rear to show at best double-yellow.
  • If both yellows fail or the red fails then the signal in rear can be made to show red and those trackside handsignalmen with their coloured flags and hand lamps then take over until the lamp changer arrives with more lamps for the fixed installation.
Re: Fail Lamp Detection.
06/03/2008 8:42 AM
Hi PW,
While i appreciate your explanations, especially on the 120 ohm resistor used as a "sucker" to bypass the self generated emf by collapsing magnetic field, i am wondering how the user selected the 120 ohm resistor.. I know it will also work without the use of the bypass resistor. By how would u go around selecting the 120 ohm resistor?
Shalom..
06/03/2008 9:14 AM
  1. What is the running current and rated voltage of the lamp?
  2. What is the running current of the lamp at 18V, allowing for any series resistance presented by cables feeding it?
  3. What is the operating current of the relay at 6V?
  4. Apply Ohms Law and Kirchoff's Law.
06/03/2008 8:58 PM
Hi PW ,
Thanks for the detailed explanation, Makes sense to me now! And Del the Cat was prophetically correct all along huh! Once again thanks for taking your valuable time to answer. It was enlightening.
Joy for u and shalom...
Moo Moo.... 6/3
06/04/2008 2:00 AM
A possible solution:
Aged man is not old man...
06/04/2008 2:37 AM
Hi Qqberci..
Thats a neat circuit..
Thanks
06/04/2008 3:23 AM
You could use a small ferrite cored hand built CT whose primary (only a couple of turns) can be put in series with the 24 Vdc supply and the lamp. If the lamp blows there will be a spike at the secondary (a few tens of turns) which can then be processed digitally to provide the required signal at a remote place.
06/04/2008 4:10 AM
Hi all,
So there must be something wrong with the second part.. in which a 2.2 ohm resistor was connected across the coil of a 12v relay to power up the 24v 45W lamp!, because the calculations doenst make sense with 2.2 ohm resistor in place.
Thanks.
06/04/2008 9:54 AM
This is a simple circuit which I have used, sorry it is on the small side cannot seem to enlarge it. 12V or 24V take your pick. Also if you wire a solid state beeper via a diode you can fit any number of these indicators and use one beeper for them all.
This method does not interfere with the lamp circuit and supply to the indicator circuit can be from a totally separate supply if required.
06/04/2008 9:58 AM
The simplest way is to buy a normally closed reed relay.
Wrap say 20 turns of wire closely around it (some come with a plastic bobbin already in place!) and place it in series with one of the leads going to the lamp.
Check the relay to see if the points are now open when the lamp is on and closed when the lamp is off. If the relay does not close, add a further 20 turns till you get reliable operation. Make sure the wire is thick enough to handle the lamp current!!
Add alarm circuit to the relays contacts so that alarm goes off when relays contacts are closed!
Reverse everything if you can only get a normally open version!!
06/04/2008 10:14 AM
Ah great minds etc.
06/04/2008 5:08 PM
I would not say my mind is great, but it does find the simple solution quite often, so you might add that I have a simple mind!!
06/04/2008 5:29 PM
Hi, to all,
It does not seem quite right to me, the small six volt relay coil would have a resistance of around forty Ohms, drawing only 0.15 A. The resistor is 120 Ohms, drawing say 0.05 A total draw 0.2 Amps. Did I see that the lamp was 24 V 45W. ?
Even at 18V it would draw over 1Amp, this would be certain death for the relay.
To stay alive the lamp would need to have a resistance of no more than 90 Ohms,or so, making it around 3.6 W.
Dave.R.