What would the GPM with a chilled water temp of 50 deg to Chilled water to cool a 250,000 BTU coil. What is the formula to estimate
Pathfinder Tags: chilled water
User-tagged by 2 users
Re: Calculating the GPM to Cool a 250,000 BTU Coil
06/05/2008 10:58 PM
Assume that the water leaving the coil is 60F giving you a delta T of 10F. Divide btu/hr by 500 and by the 10F delta, or divide btu/hr by 5000.
Good Answers: 18
06/06/2008 8:39 AM
1 BTU is the energy required to raise 1 pound of water 1 degree F.
The GPM will be dependant upon the heat transfer efficiency of your chilled water cooling process, and can't be known by someone in this forum without much more information or empirical data.
06/06/2008 10:46 AM
I assume you mean you have a coil from which you wish to remove 250,000 Btu/hr. Such a rating has to be based on some temperature difference between the media inside and outside as well as a heat transfer coefficient.
Any consistent set of units can be used. I use english units below.
The formulas you need are as follows:
Q=M*Cp*dT = U*A*dT2
M*Cp*dT is the energy transferred into the heat transfer media. You can trade-off flow for dT and achieve the same heat transfer.
U*A*dT is essentialy states the capacity of the heat transfer surface to move heat form one side to the other.
Q = heat flow (Btu/hr)
M = mass flow of heat transfer media (#/hr)
Cp = heat capacity (Btu/# F)
dT = entering temp - leaving temp
U = overall heat transfer coefficient (Btu/hr ft2 F)
A = heat transfer area (ft2)
dT2 = inside coil temp - outside could temp (use an average or log mean)
1/U = 1/hi = 1/ ho
hi = inside heat transfer coefficient
ho = outside heat transfer coefficient.
values for U, hi and ho can be estimated from relevant tables, empirically measured, or calculated. To calculate, I woudl start with the Seider Tate equation which you can find on-line.
All generalizations are false, including this one.
06/06/2008 2:01 PM
What brand of coil? Website? Books on shelf? Tables will tell pump size h.p. & g.p.m. have you people ever heard of K.I.S.S. principle. If you don't know some of the info., compare sizes, passes, etc. to Trane coil of same. They have great literature to source.