Grounding System in Class 1, Div 1 Room

06/06/2008 12:23 PM

At our plant we make products with methanol and ethanol. We have had an explosion and fire and the fire inspector has blamed the cause on a bad hose line that lost its ground. I have since found out that the grounding that we have had in place, obviously is not up to specs. I have read that we should have a resistance reading of 1 or less ohms. I have since installed a #6 wire to structural steel and water pipe and have looped the grounding cable around the mixing tanks and individualy grounded them I am getting a reading of 1, however when I attach the hose (that is wound with ss the reading goes back up to 3. I am in the process of using all ss lines thus helping the grounding issue. I will still have to use a hose for part of the process. So... is using a multimeter to test grounding ok or should I get a megger. Also what are acceptable readings. Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: El Lago, Texas, USA
Posts: 2639
Good Answers: 65
#1

Re: Grounding system in class 1 div 1 room

06/06/2008 4:20 PM

I would use a four wire Ohm-meter. Make sure that you have calibrated out the resistance of your probes.

Reply Score 1 for Good Answer
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#2

Re: Grounding System in Class 1, Div 1 Room

06/06/2008 9:21 PM

Mobile fueling trucks at US airports are required to be equipped with bonding-grounding cables. Try checking with an airport refueler at your nearest airport. If you have trouble getting the requirements, reply to me on Monday, I can find them when I go back to work. Good luck.

__________________
Bob
Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#3

Re: Grounding System in Class 1, Div 1 Room

06/07/2008 7:55 AM

Using a multimeter for low ohm readings is not the best instrument. You should use an accurate constant current supply which can be adjusted up to say 10 amp wire this to the circuit that you wish to test and measure the voltage drop across it. This confirms good connections and the volt drop measured using a reasonable quality DDM will be quite accurate.

I am not sure where you are measuring with regards to the SS hoses but SS has a high resistance relative to copper.

__________________
Dont get on to the roundabout if you dont know how to get off
Reply
Associate

Join Date: Mar 2008
Location: north east
Posts: 29
#4
In reply to #3

Re: Grounding System in Class 1, Div 1 Room

06/07/2008 9:17 AM

Don't over look any sealing compounds,if used in your piping systems

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bhankiii (1); bob c (1); dg1258 (1); garth (1)

Previous in Forum: Plating Compounds for High-Voltage Buses   Next in Forum: Where are Distance Relays Used?
You might be interested in: Air Hose and Air Duct Hose, Hose Crimpers, Hose Reels

Advertisement