Conduit Fittings

06/11/2008 2:35 AM

Hi Guys,

I have a duct mounted smoke detector with a housing made of plastic. It provided two conduit entries for its wiring.

What type of conduit/ what material of conduit fittings should I use? Plastic too? or can I use galvanized fittings also?

Thanks.

__________________
"Autobots.......TRANSFORM!!!!" -- Optimusprime
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#1

Re: conduit fittings

06/11/2008 5:49 AM

It depends on several things. Number one, do you want to run the wiring in conduit. Number two, do you HAVE to run the wiring in conduit. From personal experience, as long as you aren't going to be constantly taking it off and putting it back on, any metal conduit should work fine for you. Plastic conduit would work as well. However, I don't know what any of your electrical codes are, so it's hard to give a good answer.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Register to Reply
Active Contributor

Join Date: Aug 2007
Location: Sacramento California
Posts: 18
Good Answers: 1
#2

Re: Conduit Fittings

06/11/2008 9:35 AM

It really shouldn't matter unless you are intending to mix the conduit types and adaptor types. If you are intending on running it in pvc, then use pvc throughout. If you are intending on using EMT, then don't try to put a pvc male adaptor on the end of a stick of EMT, because it isn't intended to be used that way.

I would bet that most methods don't employ a conduit system at all, rather they use a plenum rated cable.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#3

Re: Conduit Fittings

06/11/2008 10:03 AM

Optimusprime; is the detector 24 volts or 120 volt? maybe a bushing & thermostat wire

Register to Reply
Active Contributor

Join Date: Aug 2007
Location: Sacramento California
Posts: 18
Good Answers: 1
#4
In reply to #3

Re: Conduit Fittings

06/11/2008 10:23 AM

VERY GOOD POINT! You wouldn't want to run individual conductors (for 120volt installations) without a conduit system, unless you used MC, or a Romex (type) of cable. If using a MC or Romex cable (for 120vac system) then a connector is a MUST.

Register to Reply
2
Anonymous Poster
#5

Re: Conduit Fittings

06/12/2008 8:27 AM

You use a plastic bushing and lock nut with UL listed fire alarm cable for open wiring. It should be plenum rated if it's in a return air ceiling space.

If you intend to use a raceway system, the conduit connection to the detector should be flexible conduit either metal or plastic.

In any event don't use thermostat wire. It's not UL listed the the use.

If you're located in the USA the NFPA codes usually prevail but don't forget your local building official.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#6

Re: Conduit Fittings

06/12/2008 1:41 PM

To answer the original question, is does not matter what material the connector is made of, as long as the associated conduit system meets NEC. Based on my experience and understanding of the NEC, EMT is the minimum.

After Reading some of the other posts I would also add I think PVC is not allowed in air handling spaces, so the use this type of conduit system would be excluded. Please forgive me if I'm incorrect as I don't have a copy of the NEC in front of me.

I cannot comment on the use of a cable assembly such as MC or BX cable: I don't see anything wrong with it but I have not seen it used in that application.

As far as any non-metallic clad cable assemblies, it sound suspect to me. I would make sure it is an FM approved methodology before using it.

None the less, some kind of connector would still be required, one compatible with its conduit /cabling system.

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Conduit Fittings

06/12/2008 2:10 PM

MC cable is approved for the use and UL listed and can be installed anywhere metal raceway is specified, including open to the weather with the correct weather resistant jacket.

Plastic jacketed cable such as NM is not approved. EMT is not the minimum and open wire is allowed if all the requirements of the NFPA codes are followed....and you are correct about PVC conduit in a plenum space as defined by UL (United Laboratories) and NFPA (National Fire Protection Association)

Register to Reply
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#8

Re: Conduit Fittings

06/13/2008 1:31 AM

just my two cents on a quarter.

The housing of a duct detector is not predicated by the NEC ro grounding. So the housing can be plastic. If the conductors are shielded, then they should only have one grounding point. As far as two connection points. If the system is a class "A" 4 wire then you have an in/out in case of a failure. In the case of a class "B" then the in/out can be in the same conduit; usually the case in addressable systems. hope this helps.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

EV1guy2004 (1); Lendog (1); MCofSacramentoCounty (2); perry (1); Shawn_V_Elect (1)

Previous in Forum: HT CABLE   Next in Forum: how to caculate current density

Advertisement