Calculating Voltage Drop

06/12/2008 2:40 PM

HOW COULD I CALCULATE THE VOLTAGE DROP OF 400 AMP,3PH 230V WITH A DISTANCE OF 250 LINEAR METER FROM MAIN DISTRIBUTION BOARD.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: voltage drop

06/12/2008 2:45 PM

Hello Guest,

Is this a class or homework question?

Please reply with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Participant

Join Date: Jun 2008
Posts: 1
#2

Re: Calculating Voltage Drop

06/13/2008 2:30 AM

Dear

VD % = 1.73*full load current I *( R cos Φ + X sin Φ ) *100*cable length / nominal voltage V

Regards

Aiman

Reply
Anonymous Poster
#3
In reply to #2

Re: Calculating Voltage Drop

06/13/2008 4:59 AM

Dear

VD % = [ 0.2* load current (amps) *cable length(m) *nominal voltage (Volts)] /

full capacity rated currentcable (amps) volts. : for 1 cable and 3ph 4w

balance Loasd, But on single phase or dc must be double or *2,and*1.7

for 3ph 3W

or

VD % = Load current (amps) * (cable spacific resistivity/m) * cable length(m)

remark1: cable rated current, cable specific resistance and volatage drop formular

can see factory book table! or cable catalog.

remark2: cable rated current (amps) comment from current which apply on cable at

100m length until apear voltage drop 2% of naminal voltage (Line-nuetral

or ground voltage (0 volt))

remark3: cable rated current (anps) or current duration can be comment from cable

temperature rise 5 c-degree from 25 c-degree on free air or not more 40

c-degree in conduit or wire way (close cable trend)

remark4 cable rated current (anps) or current duration can be comment from cable

temperature at 25 watt / Kg for enamale insulated wire for coil or electric

machine such as motor, gennerator and transformer

All concludsion: are the same result but different spacific comment reson.

Regard

S. Sudkaew

13/6/2008