Analyzing Cable Costs

06/13/2008 1:04 AM

actully we are doing project on "cable cost analysis of 11kv and 6.6kv".i am going to compare the 4000kw raw mill (same capacity for 11kv 6.6 kv).but the size of the cable is different like 1x120+16mm^2 2XSEY(6.6KV) and 3x150+25mm^2 2XSEY(11KV).Obiviously size of the cable should differ because of two different current rating.my question is whether can i take two different cable for my calculation or not

__________________
Knowledge Sharing
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Jun 2008
Location: Chennai
Posts: 31
#1

Re: cable cost analysis

06/13/2008 2:25 AM

Hi,

Please follow the steps:

  • First decide the voltage .
  • Then decide about the load. (4000 kW)
  • Consider the Short Circuit Rating
  • Decide about the type of cable laying
  • Finalise the cross section based on the above factors.

It is quite obivious that the cross section of 11 kV will be higher and therby cost for cable, support structure will be more.

N.Suresh

__________________
N.Suresh
Register to Reply
Commentator
India - Member - New Member

Join Date: Jun 2008
Location: Tamilnadu,india
Posts: 64
#2
In reply to #1

Re: cable cost analysis

06/13/2008 2:40 AM

Hi,

Please follow the steps:

  • First decide the voltage .
  • Then decide about the load. (4000 kW)
  • Consider the Short Circuit Rating
  • Decide about the type of cable laying
  • Finalise the cross section based on the above factors.

It is quite obivious that the cross section of 11 kV will be higher and therby cost for cable, support structure will be more.

N.Suresh

doubt:

actually the cross section of the cable depends upon the current rating.so higher voltage means it takes lesser current .Then why you said that cross section of 11 kV will be higher .current higher -cross section high-cost is high.(this is my opinion)

my question is can i take two different cable size for comparision

__________________
Knowledge Sharing
Register to Reply
Member

Join Date: Nov 2007
Location: Tianjin, china
Posts: 6
#4
In reply to #2

Re: cable cost analysis

06/13/2008 9:32 AM

Hi ,

What i understand from Mr. Nagarajan answer is , cross section of 11 KV cable is always higher than 6.6 KV cable considering cable size is same .i.e a 300 sqmm ,11KV cable have higher cross section than 300 sqmm , 6.6KV .As higher rated voltage cable require more insulation material (XLPE .. etc) so more cross section area.

Register to Reply
Participant

Join Date: Jun 2008
Posts: 4
#3

Re: cable cost analysis

06/13/2008 7:17 AM

Hi,

Well, there are some items I assumed, but the calculation is not so difficult.

Example 1:

4000kW; approx. 430A; 6.6kV; Ik= 31.5kA; cable length= 100m; CB switch off time=0.15s;
IEC/VDE regulation; ambient temperature = 45°C; cable laid on cable tray; XLPE cable multi.

Cable according to short circuit:

According to data above, the cross section of each cable must be (worst case) mind. 85mm2 resp. 95mm2 (cable type)

Cable according to load:

Reduction factor:

Laying on tray: 0.91

Temperature: 0.87

Total= 0.91x0.87=0.7917

430A/ 0.7917 = 543A è for this value you have to find a cable which is bigger than 95mm2 (short circuit)

Cable load according IEC= 3x95è 304A

Max. cable load: 2x304A = 608A

Check: 543<608

You should use two cable 3x95/16 parallel for this Motor.

Example 2:

4000kW; approx. 250A; 11kV; Ik= 31.5kA; cable length= 100m; CB switch off time=0.15s;
IEC/VDE regulation; ambient temperature = 45°C; cable laid on cable tray; XLPE cable multi.

Cable according to short circuit:

According to data above, the cross section of each cable must be mind. 85mm2 resp. 95mm2

Cable according to load:

Reduction factor:

Laying on tray: 0.91

Temperature: 0.87

Total= 0.91x0.87=0.7917

250A/ 0.7917 = 316A è for this value you have to find a cable which is bigger than 95mm2 (short circuit)

Cable load according IEC= 3x95è 304A

Check: 250<304

You should use one cable 3x95/16 for this Motor.

Last comment:

You can optimize the cable cross section if you change laying factor, temperature, etc.

Hope that the calculation is helpful.

BR

Wormnhaque

Register to Reply Score 1 for Good Answer
Member

Join Date: May 2008
Posts: 6
#5

Re: Analyzing Cable Costs

06/14/2008 7:20 AM

download from dutch side

vision

http://www.phasetophase.nl/en_index.html

configure all your cases voltage and load patterns in the demo mode

calculate loadflow an go to results (it wil do for max 20 nodes)

but your case will fit

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!