hi all
there is 3hp motor 460v 3phase, driven by 2.2kw 380/460v 3phase power inverter, the speed referance is potentiometer 10kohm.
when i turn the rheostat the motor run for 5sec then stop and the inverter display showing code means that load current exceeds the limit, actually i tested the output current from the inverter it is about 8.5amps. the inverter input current is 2.3amps
i migger the motor it is ok, the risistance of the three coils are the same 7ohm and tried it on three phase 60hz it is ok pulling about 1amp.
when i turn the rheostat even little,the motor turn and the inverter display shows 9hz output frequency and when i turn rheostat up or down it does not change the speed of the motor still 9hz until it shutoff showing over current.
also when the motor is running i hear acoustic noise like the rotor is touching the stater but when i tried it on three phase supply 60hz it is running fine with out noise, i opened the motor and found it ok, bearings ok.
now i disconnected the motor from the inverter and tried the inverter with out load, it seams to be ok, when i turn the rheostat the frequency goes from zero to maximum 100hz and the opposite.
what do you think is the problem? is it inverter problem or the motor need to be replaced?
please advice
thanks