Anonymous Poster

VCB RATING

06/16/2008 9:56 AM

.how can calcute the VCB RATINGand its settings..to our CR4 Engineering Community

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: VCB RATING

06/16/2008 10:03 AM

The rating of a VCB is not something you would calculate, it is something provided by the VCB manufacturer. If you ARE the VCB mfr and you don't know how to determine the ratings of your products, please post the name of your company so that I can completely avoid using your products!

If you are asking how to determine what size VCB to use, that is also smething so basic as to make me suspect that you are not an electrical engineer. In that case, you should hire someone qualified to do your project. VCBs are only used on very high power medium voltage or high voltage projects. If you have to ask this question, you should NOT be involved in it. For us to help you would be irresponsible.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Active Contributor

Join Date: May 2008
Location: Chandigarh , India
Posts: 11
#2

Re: VCB RATING

06/16/2008 10:19 PM

Dear ,

Normally VCBs are in rated as following

01. Voltage 12 KV,

02. Current 630 / 1240 amp.

03. Short time rating

a) Making current Normally 100 KA for 1 sec

b) Breaking current Normally 40 KA for 1 sec.

( even you can go for 25 KA rating but it all depends upon short ckt rating of your system)

Reply Score 1 for Good Answer
Associate

Join Date: Jun 2008
Location: Chennai
Posts: 31
#3
In reply to #2

Re: VCB RATING

06/17/2008 6:51 AM

Hi,

11 kV, 630 A, 11 kV, 800 A, 11 kV, 1200 A, 11 kV 2000 A , 33 kV, 1250 A, 1600 A , 132 kV, 1250 A, 220 kV, 1600 & 2500 A, 400 kV , 2000 A are available.

This cab referred from the data sheets of the manufacturer which will be indicated in the name plate details of the equipment.

N.Suresh

__________________
N.Suresh
Reply
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); Nagarajan.Suresh (1); Punit Sharma (1)

Previous in Forum: Arc welding   Next in Forum: Power transmission line

Advertisement