Vibration Interlock on a Recip

06/17/2008 9:44 AM

I recently had an "opportunity" to help out with the aftermath of a mechanical recip compressor failure and ran into something that seems strange to me.

During the failure, the vibration switch (an earthquake switch mounted on a different cylinder's distance piece) came into alarm. On most of the other recips I have been around, this would have shut the machine off immediately as a protection feature but on this one they made it an alarm only so the machine ran an extra 30 seconds or so before the operator shut it down. To me, this exacerbated the damage done to the machine and could have caused it to really fail catastrophically.

The question I have before the group is would you normally make the earthquake switch a trip or would you have it as an alarm only? The machine has a 100% spare, but no vibration trip still seems a little questionable to me. Any thoughts?

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Pathfinder Tags: Compressor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: Vibration Interlock on a Recip

06/17/2008 9:57 AM

wild guess here

The design of the switch and delay probably depends on what the pump is feeding, how critical it is, and how long it needs before it can safely be shut down. In other words the whole system is important. i.e It may be worth losing a cooling pump if it gives time for a reactor to safely shut down.

The fact they have a spare confirms, it is a critical component to some system. Not only are they willing to lose a pump, they have prepared for it.

The delay could also be put in to ensure it does not shut off for false alarms.

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Power-User

Join Date: Jan 2007
Location: The Capital City, Cow Hampshire, USA
Posts: 476
Good Answers: 3
#15
In reply to #1

Re: Vibration Interlock on a Recip

06/21/2008 8:49 AM

One would hope that it if this were the case, the system would provide excessive storage of compressed air as short-term reserve supply, Plus an auto start of the redundant unit.

With modern controls, this should be the norm.

D*mn, it should also be able to alert repairs w/out human intervention!

__________________
If you always do what you've always done, You'll always get what you've always had!
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#16
In reply to #15

Re: Vibration Interlock on a Recip

06/21/2008 9:43 AM

Knowing a bit about Betomachine from other posts, I doubt that this is an air compressor. It is most likely a large machine compressing hydrocarbon gas of some kind.

Auto start of the spare is probable in this case...

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#17
In reply to #16

Re: Vibration Interlock on a Recip

06/23/2008 11:03 AM

Truly, it is a two service machine compressing RFGA in two stages on throws 1 and 3 and compressing hydrogen in a single stage on throws 2 and 4. It is therefore one of the feed compressors to the hydrogen plant and the product compressor at the same time.

Sadly, due to the sensitivity of some of the other controls around the unit, the auto start functionality is not typically used since it tends to cause issues up and down stream of the compressors.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#2

Re: Vibration Interlock on a Recip

06/17/2008 10:36 AM

On most equipment, so called "safety devices" Jam relays, SMC's overload protection devices, limit switches etc. are there to protect the equipment by limiting the time damage may occur. Having a backup compressor, I would rather have the equipment shut down as soon as possible. I would then switch to the backup and proceed to test, inspect and monitor the failed device to identify if it needs replacing, calibration or repairs. If a critical unit shuts down and I can quickly and safely switch over to a backup, I will in most cases be able to facilitate repairs and get the unit back on line with less downtime and less expenses. When you kick up a stone while driving your car and your oil light comes on, do you pull over right away or do you drive home to your garage and check it out later? Better to replace an oil pan then the entire engine.

If the compressor needs to run to shut down the operation correctly and safely I would consider installing a failsafe device to switch over to an air storage tank, while still shutting down the compressor, that would supply enough air to the unit for the time needed to stop.

Alarms are always good to have to tell the operators "YOU HAVE A PROBLEM!! CALL MAINTENANCE!!" I would make sure the equipment could not be started until the tech could unlock the controls and preset the equipment after assessing the situation.

Then again, maybe the switch was wired incorrectly and not detected until it was needed. The proverbial OOOPS!

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Register to Reply
Anonymous Poster
#3

Re: Vibration Interlock on a Recip

06/17/2008 2:30 PM

Believe you me... as some of my pal's used to told me long ago which I'd always found out very funny expression from their part definetly. I may tell ya' one or two things from few headaches with such puppies before. Let it alone the 'Full Moon' effect for the moment, the vibration stuff do play some kind of foolishment into this kind of troubleshot definetly, I agree. I did saw equipments sometimes with such troubles before couples of times and apparently after monitored the conditions for some time it came down to few different circumstances of operations by the way.

Equipment installed without vibrations reducing features on framing base and piping like say, And electrical signal conditioners systems around to minimized line noises, armonics and stuff. Also good to watch out for those neutrals / returns wirings since as they become loose or make bad contacts somewhere due corrosive effects or so forget it, it dont take much to cause some difficults as well.

Allset, Lock and Tag,

MC

Register to Reply
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#4

Re: Vibration Interlock on a Recip

06/17/2008 4:14 PM

Steve S

Aren't the new switches still referred to as earthquake switches, but just changed from the old mechanical to electronic. I guess they could be called different things for different circumstances. We do use the electronic for protective devices. Maybe were just used to the old vernacular and stuck in our ways.

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#6
In reply to #4

Re: Vibration Interlock on a Recip

06/17/2008 4:52 PM

Typically, when you speak of an earthquake switch, what it means is a mechanical switch, either of ball in socket type where the vibs get high, the ball falls out and the switch goes, or a simple spring loaded arm sort of switch like the one Betomachine is using.

A piezo accel based transmitter could I suppose be called an earthquake switch, but the reliability is better, the frequency response is better, and there are no moving parts. I would call it a vibration transmitter not an earthquake switch..

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#5

Re: Vibration Interlock on a Recip

06/17/2008 4:40 PM

I call it an earthquake switch because it takes an earthquake to set it off and then it has to be reset in the field. The switch comes into the DCS as a discrete on/off. I would prefer a 4-20 signal so I can see things and I think that Steve S. is suggesting that as well. I've also seen similar switches "calibrated" with a heavy hammer hitting the frame next to them to be sure that they will actually trip.

I checked 618 and the way I would read it is that you need something a little more transparent than a switch as it calls for continuous measurement, alarm, and shut down features.

We have put online monitoring on a couple machines in our fleet with vibration monitors on the crossheads with some success/failure as well. One machine in particular tripped quite frequently but it was in a chlorine battery offgas service and saw a lot of moisture and particulates. This led to a lot of "spurrious" trips. The other one is in a clean gas service and does fairly well.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#7
In reply to #5

Re: Vibration Interlock on a Recip

06/17/2008 4:59 PM

Yep this is a mechanical switch of the type specifically excluded in API 618.

Paragraph 7.6.7.1 in the 5th edition states: The device and its mounting shall conform to API 670. Ball-and-seat or magnetic-type switches are unacceptable.

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#8
In reply to #7

Re: Vibration Interlock on a Recip

06/17/2008 5:04 PM

So you would say that this meets the letter but not the spirit of 618?

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#9
In reply to #8

Re: Vibration Interlock on a Recip

06/17/2008 5:18 PM

No, no, your device is specifically not allowed by API..on a new machine anyway...

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#10
In reply to #9

Re: Vibration Interlock on a Recip

06/18/2008 8:49 AM

OK, thanks for the guidance on this, I appreciate it.

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Anonymous Poster
#11

Re: Vibration Interlock on a Recip

06/18/2008 9:15 AM

We have set all of ours to trip the compressor

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#12

Re: Vibration Interlock on a Recip

06/18/2008 11:38 AM

Thanks for the Metrix link. I am trying to decipher what I need for an axial fan setup for fan vibration and bearing condition detection. Spec calls for "shock poulse measuring bearing damage" and "fan vibration monitoring . . . to trigger . . . two levels of vibration: alert and alarm".

Any cheap advice?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
2
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#13
In reply to #12

Re: Vibration Interlock on a Recip

06/18/2008 1:12 PM

I like this gizmo for your application:

http://www.reliabilitydirectstore.com/CMCP-1000-Explosion-Proof-Vibration-Monitor-p/cmcp-1000.htm

And if you look around the site you will find other multichannel options as well. The only problem is if the spec specifies shock pulse monitoring, then you are stuck going to SPM company.

http://www.spminstrument.com/

I might take exception to the shock pulse monitoring requirement. Any company that does high frequency enveloping is more or less doing the same thing.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#14
In reply to #13

Re: Vibration Interlock on a Recip

06/18/2008 3:48 PM

You're a gentleman and a scholar. Thanks for replying to a somewhat "off-topic" question!

Ried

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); betomachine (4); charsley99 (2); Ried (2); sidevalveguru (1); Steve S. (5); techno (1)