Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/17/2008 4:09 PM

Hello,

Thank you for taking the time to participate! I have collected a dataset of the line voltage and frequency on a bus while a high power motor was started. The motor in question is a 5300hp synchronous motor.

The bus voltage dropped to 89% of nominal and while the voltage was rising there was one cycle where measurements show a frequency of 0 Hz. This anomaly was present in two datasets taken from the same bus by two separate multilins.

I was not aware that the frequency of a 4160V 3 phase bus could be forced to zero. I do not see any information on the web. Would anyone be able to shed light on this mystery.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/17/2008 7:49 PM

Slip a pole?

Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2
In reply to #1

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/17/2008 7:50 PM

OOOOPs--Slip a pole??

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/17/2008 9:00 PM

That can happen at pull-in, i.e. right when the field application relay closes to apply the DC to the rotor windings. Not supposed to, but it does.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#4

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/17/2008 11:52 PM

Besides the possible reasons suggested by other friends, I feel the frequency measuring instruments can give erratic readings especially during the supply waveform clamping which is likely to incur during start-up of the heavy motor. The chances of this are more likely if the two separate multilins reffered above are of same type and brand.

In fact, the frequency cannot go to zero for the un-interrupted AC source for only one cycle especially while the AC Voltage is present and is recorded by the Voltage measuring instrument.

__________________
Karma is Dharma
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/18/2008 2:57 AM

Perhaps it may be better repeat the test with another set of instruments.Frequency normally cannot go to zero on a infinity source.By the way what is the source?Thanks for bringing this to the forum.We may all gain some thing and have some interesting points in this thread.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Associate

Join Date: May 2008
Posts: 50
#6

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/18/2008 5:30 AM

Dear Sir,

The " Zero Hz " frequency phenomenon, so far , as major grid system to which your electric machine is connected is not possible SIR.

Otherwise the cascade tripping is just enevitable.

Regards,

Ulhas Pradhan

Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#7

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/18/2008 7:51 AM

From my experience with Multilins the sampling time sometimes is not adequate to record high speed events in power systems.. As suggested obtain a high speed power monitor and try again..

Also, are the Multilins powered from DC source, or from the CPT in motor starter.. If CPT, the voltage dip / or surge, could cause the trending data in Multilin to become unreliable..

Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#9
In reply to #7

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/19/2008 2:04 PM

GA - I agree as this has also been my experience with GE Multilins. I wonder what kind of starting scheme is being used...

Reply
Anonymous Poster
#8

Re: Voltage and Frequency Affected by 5300-hp Sync Motor Start

06/18/2008 8:35 AM

Say there dude, did you check to see if your instrumrntation will operate properly at 89% voltage? Got a battery powered model? Give that a try. If that still gives you the same result then you have indeed slipped a pole. No biggie.

Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); chhotu1990 (1); ekiechle (1); JRaef (1); Kilgore Trout (1); Lendog (1); nesubra (1); umpradhan (1)