I would like to know how to calculate the full load current and lock rotor current of a 3-phase motor ,480V, 62% efficiency and 84% power factory?
Good Answers: 804
Re: Calculating Current for Three-Phase Motors
06/17/2008 6:56 PM
Full load current is not calculated, it is measured. The other data is calculated from that.
06/18/2008 2:51 AM
Kw Of Motor/Voltage in KV*Power factor*1.732*motor eff
06/18/2008 3:00 AM
FOR CALCULATING FULL LOAD CURRENT, YOU MUST HAVE OUTPUT POWER RATING OF THE MOTOR WHICH YOU HAVE NOT GIVEN. Assuming that 84% is power factor (0.84) in place of power factory (if i am right).
AFTER GETTING POWER RATING
USE SIMPLY THE FORMULA
I(full load) (line current) = P(output) / (Sq. root (3) x V(line) x p.f x efficiency)
06/18/2008 7:35 AM
As a rule-of-thumb, lock-rotor current exceeds full load current by a factor of 5.