Substation Ground Grids

06/17/2008 1:41 PM

Our client requires the substation ground grid to utilize insulated 4/0 copper. My question is. Is the copper cabling for the grounding itilized in the overall grounding calculation, and if so, the unsulated copper would directly affect this calculation? Would the insulated copper help extend the lifespan of the conductor from contaminants possibly? I can not seem to get a definite answer from them?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Substation ground grids

06/17/2008 3:47 PM

Is your client a power company? Using insulated conductors in the ground is counter to what the grid is for! Using insulated conductors connected to the uninsulated grid protects the above-ground conductor from the elements.

I'd check with the client or the engineer who more than likely mis-specified insulated ground grid.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#2

Re: Substation Ground Grids

06/18/2008 9:18 AM

Highly unusual request.

I have seen many power plants and hundreds of substations but never insulated conductors.

You need to be careful in the type of copper you use.

Our standard is for compact copper

Register to Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#3

Re: Substation Ground Grids

06/18/2008 11:39 AM

The purpose of a ground grid is to get as much contact as possible between the grid (copper conductor) and earth as possible to achive a low earth-ground resistance. Having an insulated condutor completely defeats this purpose.

Register to Reply
Participant

Join Date: Jun 2015
Posts: 1
#4

Re: Substation Ground Grids

06/29/2015 8:15 AM

actually insulated grids are used sometimes. you need to know the soil. if there is high levels of chlorides and/or sulfates, low resistivity, etc, then the copper grid can actually corrode quickly... frequent ground rods are used with an insulated grid.

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (1); jdcpe17 (1); Lendog (1)