Turbine expansion problem

06/22/2008 5:28 AM

When we assemble the turbine the total axial float was 5.0 mm and all the radial and axial clearances were as per our site protocol.In this condition when rolled the turbine and synchronised there was no problem in expansion.The total shell expansion was 12 mm which was good as per designer but when the turbine tripped the turbine came to halt and significant vibration was observed in Front bearing.Till now we are not able to rotate the turbine even by manually also.

Please suggest.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
United States - Member - US Navy Veteran

Join Date: Mar 2007
Location: Nothing sucks more than that moment during an argument when you realize you're wrong.
Posts: 301
Good Answers: 22
#1

Re: Turbine expansion problem

06/22/2008 9:17 AM

Try this link.

http://www.turbinegenerator.com/askaquestion.asp?expert=0

=====================================

TGM's Corporate Office is located in Cape Coral, Florida.

TGM has a logistical center located in Knoxville, Tennessee

1490 NE Pine Island Road, Suite 5e, Cape Coral, FL 33909-2127
Main Office 800-226-7557 | Hotline: 888-MrTurbine (678-8724)

__________________
You never know when it will strike, but there comes a moment when you know that you just aren't going to do anything productive for the rest of the day.
Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#2

Re: Turbine expansion problem

06/22/2008 9:32 AM

Were the diaphragms pulled out during the outage? Sounds like a diaphragm might have broken loose and jammed the machine.

The other possiblity is that you threw some blades and they jammed up between diaphragms and seized the machine..

If the axial floats and shell expansions were all ok and the machine was running ok, and now the machine wont even turn over, something serious happened.

One way or another I would suggest that you will have to pull the lid and have a look.

Register to Reply
Power-User
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2006
Posts: 451
Good Answers: 16
#4
In reply to #2

Re: Turbine expansion problem

06/23/2008 1:45 AM

I am with you Steve S. If it is jammed there is no choice but to lift the lid and check. It may well be worth lifting the bearing cap first if that was giving some indication of problems. It is a cheap option that will have to happen so it might as well be first and pray that that is all it is. One wiped bearing.

Was there much noise when the turbine tripped?

BAB.

__________________
Make it so.
Register to Reply
Anonymous Poster
#5
In reply to #2

Re: Turbine expansion problem

06/23/2008 4:27 AM

After tripping again we have checked the axial float and it is 4.8 mm till now.Is there any possibility to pull or push the turbine casing by Main steam pipe line if there is some parallelity disturbance between casing flange and MS pipe flange?Though the casing locking clearance axial and radial both was within 0.05 to 0.08 mm then why the casing centring again and again being disturbed?

Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#6
In reply to #5

Re: Turbine expansion problem

06/23/2008 7:37 AM

Not sure I understood the question, but it is possible for steam piping to push the case around, assuming that either the growth of the steam piping is not being properly restrained and controlled, or the turbine case is not properly pinned or guided.

One of the first easy things you can check is to make sure the slides and guides under the turbine case are free and allowing movement and not jammed up, they also go back to the piping drawings and make sure that spring can settings are correct on the steam piping, and if there are any slides or guides supporting the steam piping that they are free and not jammed.

Register to Reply
Member
Engineering Fields - Piping Design Engineering - New Member

Join Date: Jun 2008
Posts: 5
#3

Re: Turbine expansion problem

06/23/2008 12:23 AM

Hi first question would be when you powered up the turbine and came through the critical vibration stages did your terchnicians notice anything unusual?

Have the emergency lubrication pumps and lines been checked for integrity? are these working and is there lubrication oil in the system. Have seen it done that technicians forget the most important part of the process.

what were the temperature devices measuring at the time of your trip? along the generator? did they notice anything unusual? how long after synchronisation did the unit seize up and trip?

Register to Reply