Ventilation area (opening) calculation for generator room

06/22/2008 5:32 AM

I am sure many of you must have been involved in designing engine rooms for generators.

There is a requirement to make a building to house 8 generators ( 3512BTA Prime rated) Caterpillar make in a room.

Now, has anybody worked on designing the ventilation opening for engine room.

Some inputs,

a) The ambient temperature is 48deg C (peak) and the each generator has total heat reject (engine plus alternator) of 200kw

b) Each radiator sucks out 1641 m3/min out of the room.

c) Each engine requires 117m3/min for combustion.

d) L x b x h ( in metres) for each generator is 5.2 m X 2.28 m X 2.36 m

Now, based on these inputs what will be total opening area ( for ventilation plus combustion air required ?

Secondly what will be the overall dimensions of the room ( for 8 gens)?

Cheers,

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Participant

Join Date: Apr 2008
Posts: 3
#1

Re: Ventilation area (opening) calculation for generator room

06/22/2008 11:02 PM

Hi,

I am also involved with more or less the same thing at present;it is a ship as compared to your building.If you can access ISO8861 OR go to the google book and type for "Engine room ventilation in diesel engined ships" , this shall lead you to a book where you can find ditto example for your case.I am sorry I could have helped more but the excerpts of the book can not be copied!!! At least I could not manage.

Sincerely,

jawad

Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#2

Re: Ventilation area (opening) calculation for generator room

06/23/2008 3:27 AM

I would suggest that you have a clear 6 feet space all the way around each of the generators.

That way you would have heat exchange and fresh air flow from the vents.

Plus the 6 ft would give maintance enough room to work or a forklift to pickup to remove.

where yhou mount the disconnects will make a difference too. I would mount the disconnect near the front but to the side of each generator.

__________________
If you never do anything you never have problems.
Register to Reply
Active Contributor

Join Date: Jun 2008
Location: Geneva, Alabama (USA)
Posts: 10
#3

Re: Ventilation area (opening) calculation for generator room

06/23/2008 9:18 AM

Yes, you will need to allow for plenty of room between the generators for both ventilation and maintenance equipment.

There are some other things you may want to take into account.

1. Are you using an exhaust system or do you plan on using louvers to allow for airflow through the room?

2. How many walls will you be able to put louvers in?

3. How many walls you can use in addition to the airflow requirements of the generators will play a part in determining the size of the louver. You may need to talk with an Engineer to check out all these factors.

4. Do you want the louver to also keep as much water out as possible in case of severe weather?

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#5
In reply to #3

Re: Ventilation area (opening) calculation for generator room

07/05/2008 8:54 AM

Tclark,

1. No exhaust sytem, the radiator fan will do the exhaust as it is flush with wall.

2/3. Only one wall ( the wall opposite to the radiator will have louvers)

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jun 2008
Location: Geneva, Alabama (USA)
Posts: 10
#6
In reply to #5

Re: Ventilation area (opening) calculation for generator room

07/07/2008 8:49 AM

Chaterpilar,

I'm not sure on what size to recommend for the room. Dadw5boys recommended 6ft around each generator to allow for maintenance and forklifts. You will need to find out how much room is available to you for the generator room addition in order to design a proper layout of the room. You wouldn't want to design a room larger than the space allocated for it. Since the fan is only going to be on one wall you probably need to lay out the generators in such a way as to get the best airflow through the room once you find out what the maximum allowable size of the room will be. I also noticed that you are in Saudi Arabia, are the walls with ventilation going to be exposed to the elements such as wind driven rain or sand? If so you will need to take this into account because you don't want water or sand getting to your generators.

Hope this helps.

Register to Reply Score 1 for Good Answer
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#4

Re: Ventilation area (opening) calculation for generator room

06/23/2008 11:17 AM

I prefer for this type application a forced air ventilation system, always maintaining a positive pressure differential in the room. Also, Caterpillar, in their documentation, provides minimal design requirements.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#7

Re: Ventilation area (opening) calculation for generator room

07/20/2008 9:55 AM

Rule of thumb:

Area of air intake, 150 % of the radiator surface area for each unit.

Register to Reply Score 1 for Off Topic
Participant

Join Date: Nov 2008
Posts: 1
#8

Re: Ventilation area (opening) calculation for generator room

11/30/2008 11:25 AM

for normal ventilation :5 ACPH air flow is required for generator room

I prefere to provide positive pressure to avoid any dust entering the room

for operation time : Motorized damper and acoustic intake and outlet should be provide

the area of louvers should be applicable to pass the air flow under maximum velocity 600 FPM

__________________
Senior Mechancial Engineer
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); chaterpilar (1); cwarner7_11 (1); dadw5boys (1); h088 (1); muhammad jawad majid (1); tclark (2)

Previous in Forum: Turbine expansion problem   Next in Forum: Root Valve

Advertisement