Vapor barrier

06/24/2008 9:24 AM

Regarding Insulation :

Hi all ,

In cold insulation there is one concept called vapor barrier . I want to know how to check the Vapor barrier thickness coz the product data sheets describes that XXXX DFT .How to ensure that xxxx DFT is applied over the insulation material .Kindly provide the details .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#1

Re: Vapor barrier

06/25/2008 6:22 AM

checking my libary will get back soon.

__________________
If you never do anything you never have problems.
Register to Reply
Power-User

Join Date: Sep 2007
Location: Brampton, ON, Canada
Posts: 218
Good Answers: 3
#2

Re: Vapor barrier

06/25/2008 7:06 AM

We produce vapour barrier here in Canada. The thickness of the material can be measured by weighing the material. Take a known length (in our plant we use one metre) and weigh it. The specific density of PE which is the material we use is approximately 0.92. Our vapour barrier is 0.006" thick. For a 102" wide vapour barrier, 1 metre long and 0.006" thick, the sample should weigh approximately 365 grams.

The protectant is blended in with the polyethylene, so it is evenly distributed throughout the plastic.

In Canada these specifications are controlled by a standards board.

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Vapor barrier

06/25/2008 7:32 AM

Hi , Thkx 4 ur comment . I do agree with ur comment . It can be done for a sample test. but when it is applied on the equipment .How can u ensure the DFT xxxxx mm . Here we are using Foster 60-38 as our vapor barrier . It comes in mastic form .So when we apply over the equipment and over the reinforcement we have to ensure that DFT is 1.2 mm to ensure the water vapor permeability of 0.018 perms . So kindly provide any information u have . Regards Earnest.