Fire Protection in Computer (IT) Server Closets

06/26/2008 10:07 AM

According to industry standards and the NFPA what level of fire protection is required in telephone or computer closets (apprx. 10' x 5' space).

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2006
Location: "Dancing over the abyss."
Posts: 4884
Good Answers: 243
#1

Re: Fire Protection in Computer (IT) Server Closets

06/26/2008 11:24 PM
__________________
People say between two opposed opinions the truth lies in the middle. Not at all! Between them lies the problem, what is unseeable,eternally active life, contemplated in repose. Goethe
Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#2

Re: Fire Protection in Computer (IT) Server Closets

06/27/2008 2:40 AM

Ask yourself this question: What is the effect on my business if fire would happen in the server room?

At which speed can you replace all equipment and what amount of data is lost?

At the end of this evaluation you will have to decide: is the money invested in fire suppression worth the risks we take.

Just one advice for the future: Inergen

__________________
"Here we are now, entertain us"
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#3
In reply to #2

Re: Fire Protection in Computer (IT) Server Closets

06/27/2008 3:02 AM

Inergen is a really excellent solution.

__________________
Aged man is not old man...
Register to Reply
Anonymous Poster
#15
In reply to #2

Re: Fire Protection in Computer (IT) Server Closets

08/04/2008 2:15 PM

But think further and the words "switch from Inergen to ProInert, the superior technology" will be the new message.

:)

Register to Reply
Commentator
Hobbies - HAM Radio - New Member

Join Date: May 2005
Posts: 56
#4

Re: Fire Protection in Computer (IT) Server Closets

06/27/2008 8:55 AM

NFPA 75 tells you all about it. Look at 4.1 and 4.2. It all depends on the risk factor. Here I sprinkle all new comm closets where a sprinkler system exists in the building.

Register to Reply
Participant

Join Date: Jun 2008
Posts: 4
#5
In reply to #4

Re: Fire Protection in Computer (IT) Server Closets

06/28/2008 1:00 AM

Yes, but the sprinkler should carry dry and non conductive material, refer to Ansul site.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: "Dancing over the abyss."
Posts: 4884
Good Answers: 243
#6
In reply to #5

Re: Fire Protection in Computer (IT) Server Closets

06/28/2008 4:01 PM

Thanks MN Hague. Water + Servers doesn't give me a good feeling.

GA

milo

__________________
People say between two opposed opinions the truth lies in the middle. Not at all! Between them lies the problem, what is unseeable,eternally active life, contemplated in repose. Goethe
Register to Reply
Participant

Join Date: Jun 2008
Posts: 4
#8
In reply to #6

Re: Fire Protection in Computer (IT) Server Closets

06/30/2008 2:28 AM

May I propose Novec 1230 Fire protection fluid. This is dry and works on heat absorbtion.

Register to Reply
Commentator
Hobbies - HAM Radio - New Member

Join Date: May 2005
Posts: 56
#10
In reply to #6

Re: Fire Protection in Computer (IT) Server Closets

06/30/2008 2:03 PM

This has been discussed many times with computer folks and others. The consenious is that water damage can be taken care of and will cause less of a problem on cards than some other solutions. Thus I have gone with their recommendations.

Register to Reply
Participant

Join Date: Jun 2008
Posts: 4
#13
In reply to #10

Re: Fire Protection in Computer (IT) Server Closets

07/01/2008 2:42 AM

All the best.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#7

Re: Fire Protection in Computer (IT) Server Closets

06/29/2008 10:24 AM

We use halon in our control, server and computer rooms. There is a warning that goes off for 15 seconds in rooms that are occupied telling people to get out. Warning lights and chimes alert people that there was a discharge in the room and entry can only be done with air packs until room is cleared and refreshed. Scott air packs are stored right outside these rooms in case emergency entry is needed to retrieve any personnel that may not have gotten out. We run fire drills to make sure everyone knows the procedures and have them posted in all locations to remind them.

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#9
In reply to #7

Re: Fire Protection in Computer (IT) Server Closets

06/30/2008 2:32 AM

Halon should not be used anymore.

The Halon group of chemicals are known to be heavy contributors to the ozone depletion.

Use CO2, Inergen or whatever inert system you can get.

__________________
"Here we are now, entertain us"
Register to Reply
Commentator
Hobbies - HAM Radio - New Member

Join Date: May 2005
Posts: 56
#11
In reply to #9

Re: Fire Protection in Computer (IT) Server Closets

06/30/2008 2:05 PM

We got rid of Halon years ago.

Register to Reply
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#12

Re: Fire Protection in Computer (IT) Server Closets

06/30/2008 5:18 PM

If you are just using the closet as a rrouter layer thenyou aren't required to have any fire protection. I would suggest a high temp smoke at the minimum, the high temp is for the rising heat from the router. If over 185 typically certain smokes will go into alarm.

If however the room will house a server and UPS system, then depending on the authority having jurisdiction you might be required to have a smoke and sprinkler head in the "closet"

Depending on how valuable your equipment is I might suggest a pre-action system, contact your local sprinkler shop for details for just google pre-action systems.

Register to Reply
Anonymous Poster
#14

Re: Fire Protection in Computer (IT) Server Closets

07/05/2008 12:40 AM

Friends,

Here in Asia we would use FM200 total flooding fire suppression system from (kidde ECS Series fire suppression system by kidde-Fenwall Inc)

The extinguishing agent shall be FM200 (Heptafluoropropane)

hope that helps

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); charsley99 (1); EV1guy2004 (1); Gwen.Stouthuysen (2); Milo (2); MN Haque (3); N5EBA (3); Qqberci (1)