System Grounding

06/26/2008 8:43 PM

anybody help me please...

when we applied Solid Grounded, Resistance Grounded, Reactance Grounded and Ground Fault Neutralizer

thank you very much

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: System Grounding

06/26/2008 9:48 PM

Hello Guest,

There are so many variables, you need to narrow the scope of your question.

Please reply, with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Participant

Join Date: Jun 2008
Posts: 2
Good Answers: 1
#2

Re: System Grounding

06/28/2008 2:48 AM

You may be referring to grounding transformers? If so please consider the following:

> For Zigzag Grounding Transformer: the neutral of a zigzag transformer must be solidly grounded when applied to low voltage system, while it must be resistance grounded when used in medium voltage system.

> Wye-Delta Grounding Transformer: The wye-side must be connected to the line with the neutral grounded through a resistor. The delta-side must be closed to provide a path to the zero sequence current.

> Solid Grounding: Applicable to low-voltage and medium voltage systems greater than and including 13.8KV.

> Resistance Grounding: Applicable to medium voltage systems below 13.8KV

i. Low-resistance Grounding: Used to limit ground fault current to 200 - 400 amperes.

ii. High-resistance grounding: Used to keep a faulted feeder functioning during a ground fault until an orderly shutdown of equipment can be effected; and to keep the ground fault related damage to minimum.

Hoping this simple reply will help you. Good day to you.

Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#3

Re: System Grounding

06/28/2008 11:19 AM

The question about Grounding is further discussed on another thread under the title Earthing and Grounding, or something like that. Sparkstation gave a great answer and the discussion goes on to mention isolated grounding, wire coding, and other nuances. The new CR4 member who responded spoke of grounding in ways I have no experience with, but found fascinating.

__________________
You don't get wise because you got old, you get old because you were wise.