i measured voltage between Earth and neutral, it is 2 volts,How it to reduce to zero volts. and why voltage exists between. can any one help me ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - New Member

Join Date: May 2006
Location: Montreal, Canada
Posts: 632
Good Answers: 11
#1

Re: ee

06/27/2008 11:22 PM

Neutral is not supposed to be at 0V to ground.

Neutral carries current in a wire that has some resistance, creating a voltage drop.

V=RxI

Neutral is a return line as ground is a guard.

Not to be confounded or interchanged.

__________________
''What the hell has my a** got to do with magic?" Don Quixote
Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2007
Posts: 55
#2

Re: ee

06/28/2008 11:42 PM

Nurtural and ground are not the same thing. The green wire or round pin on the plug is a safety ground and should be solidly wired to every piece of metal in the curict and back to the pannel to and tied to the ground rod.[p]

The return or cold side of a 120 volt outlet completes the circuit for the hot side back to [from your point of view] to the power plant. Depending on what kind of service come into the panel the return can be actually made several ways. It is different for single phase which has a return wire that is very close to ground potential and 3 phase with doesn't have a leg at ground potential.[p]

However at the outlet and the panal the return wire and the safety ground should both be very close to the same and close to ground potential[voltage] of a rod driven in the ground.[p]

The most likely reason for there being a difference is the safety ground wire is not connected at some point. A two wire extension cord or plug with the safety wire prong cut off are the most likely suspects. Power wires wrapped around each other make transformers and can show several volts if you use a high impedance volt meter.[p]

Past that you probably need someone with more knowledge than you to test things out beyond testing the outlets and seeing of the ground rod at the service entrance is connected. While its not dangerous if you know what your doing it can be fatal if you don't.[p][p]

GC

Reply Score 1 for Good Answer
Associate

Join Date: Apr 2008
Posts: 28
Good Answers: 2
#3

Re: ee

06/29/2008 7:11 AM

The neutral bus should be grounded to a rod driven into the earth at least to a level of permanent moisture. If your ground rod is not sufficient the neutral will be carrying some voltage back to the nearest ground - probably at the meter pole or even the transformer pole.

Reply
Anonymous Poster
#4

Re: ee

06/29/2008 5:41 PM

Where on the system did you meaqsure this 2 V.?

Unless the load on the system is perfectly balanced there will be some 'return' current
somewhere on the neutral. You could very well be reading the result of a 'resistance to ground' path..

Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#5

Re: ee

06/29/2008 8:32 PM

In the single or three phase system? Nominal/rated voltage?

Some Current is in the neutral wire.

Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#6

Re: ee

06/30/2008 6:53 AM

first check the earth value of your earth pits it should be less than 0.5Ohms since you mention you are getting 2V between Neutral and earth immediately add plenty of common salt and leave a Water pipe with tap open for at least one hour mean while check the soil chemistry of your earth pit location and check earth values of the soil with three probe earth tester based on the values or if the earth Resistance is more than three ohms you need to keep your earth watered every day or suggest you refill your earth pit with Bentonite instead of earth bentonite retains moisture and improves soil conductivity you need to act immediately or else ask for troubles including electrocuting some one.we can discuss every aspect earth system latter

crm

__________________
Run silent run deep
Reply
Anonymous Poster
#7

Re: ee

06/30/2008 7:13 AM

The voltage measured on the neutral conductor is dependent on two factors:

  1. The amount of current being drawn by a load
  2. The distance from the ground bus at which the voltage measurement is made.

With no current being drawn by any device, there should be no potential difference between the two.

Reply
Commentator

Join Date: Jun 2008
Location: kolkata
Posts: 63
Good Answers: 2
#8
In reply to #7

Re: ee

07/03/2008 6:22 AM

Change zero setting of your multimeter. so 2V will show zero !

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ab72756 (1); Anonymous Poster (1); chakraborty ranabir (1); crm (1); gigaconcept.com (1); Gordon Couger (1); southern123 (1)

Previous in Forum: DC Motor Problems   Next in Forum: Software solutions

Advertisement