Anonymous Poster

problem

06/30/2008 1:06 AM

hi to everyone!

got a problem with an equipment having a frequency converter drive. it keeps on tripping with an it indication when the speed is adjusted to 60%. had tested the motor from another supply and found normal. i'm not so familiar about this type of equipment so i would be thankful if anyone could help me out of this one.the drive is cegelec model 4006B. the motor is a 2.2kw

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: problem

06/30/2008 7:59 AM

It is important to consider the characteristics of the load as well. Is the motor compatible with the load characteristics at 60% speed? What current is it pulling at 60% speed, and does this figure exceed the current setting for the drive?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Associate

Join Date: Mar 2008
Location: north east
Posts: 29
#2
In reply to #1

Re: problem

06/30/2008 6:48 PM

What is the fault code,High output current?output fault to ground? high DC buss voltage? there are a few reasons for an inverter to trip,Is it clean?getting hot at 60% load.There should be a fault code listed,and many have a fault history you can check.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: problem

07/01/2008 1:29 PM

I believe he was saying it is an "It" indication, meaning "I" as in Current and "t" as in thermal (in typical VFD parlance). That means it is likely a Motor Overload condition.

What you (Guest 1) may not realize is that when reducing the speed to 60%, you are reducing the absorbed power to 60%, which means the mechanical output power is also at 60%. Most loads look for constant torque, but IF your load is such hat you need constant power, you will overload the motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply