Anonymous Poster

GFCI

07/01/2008 2:56 AM

I want to know more about GFCI (ground fault circuit interceptor) to be used in my new flat and also how is it different from ELCB (earth leakage circuit breaker). Can the ELCB substitute GFCI ? or both are required independent of each other? Thanks in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#1

Re: GFCI

07/01/2008 5:25 AM

Basically, a GFCI is designed to trip when the current going through your hot wire is unequal to the current going through the return wire. If the current is not going through the return wire then the GFCI trips off, usually rather quickly and definitley more quickly than a circuit breaker will trip. I believe an ELCB is basically the same thing, only it doesn't trip quite as quickly as a GFCI. As to whether you need one or both, you will have to check with your local electrical regulations as to what is required.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Reply Score 1 for Good Answer
Participant

Join Date: Jun 2008
Posts: 4
#5
In reply to #1

Re: GFCI

07/02/2008 12:05 AM

Hi Shawn with the ELCB, it has a built in delay with a required MA draw, to stop spurious trips, also they are operated Hydraulically, so they are very quick faster then a small relay typically 20ms. I would guess the reason for this device, is that the earth is link to the zero volts or neutral. Or the transformer has a center tap config.

Reply
Anonymous Poster
#6
In reply to #1

Re: GFCI

07/02/2008 12:49 PM

I don't think a GFCI compares the potential difference between the hot leg and the common leg.

I think the GFCI compares the potential between ground and common. There should be no potential between ground and common (afterall, they are tied together at the load center).

One GFI I looked at was little more then a Wheatstone Bridge which is built with 4 diodes.

The GFI does not care about current, it only looks at potential (voltage).

Travis

Reply
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#7
In reply to #6

Re: GFCI

07/02/2008 12:57 PM

The way it was explained to me (I haven't taken one apart myself) is that there is a current sensing device between the common and hot lines. The GFCI checks for a difference in current between the two and if there is a difference then the GFCI trips. There may be other types, but I haven't taken any time to check.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Reply
Active Contributor

Join Date: Jun 2008
Location: New Jersey, USA
Posts: 22
#9
In reply to #6

Re: GFCI

07/03/2008 8:31 AM

The ones that I have seen look at the current. The Hot and Neutral wires are run thru the same toroid but in opposite directions. If the currents in the two wires are equal, their induced fields in the toroid cancel each other out. If a short occurs, the Neutral current will be lower and the field in the toroid is detected tripping the circuit.

Reply
Participant

Join Date: Jun 2008
Posts: 4
#2

Re: GFCI

07/01/2008 6:54 AM

sounds like someone is giving you a good sales pitch, or have they been watching some si-fi?

Reply
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#4
In reply to #2

Re: GFCI

07/01/2008 9:02 PM

Nope, just the voice of experience. Trust me, I'm not out to sell anything. On a more personal note. I'm not all that in love with ELCB's. I saw someone get seriously shocked by a system that was on an ELCB. I'm talking emergency room, burns, heart fibrilation, the whole nine yards.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#3

Re: GFCI

07/01/2008 10:06 AM

In most applications GFCI have replaced ELCB. You will still need to look at local electrical codes to see whats required and acceptable.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Participant

Join Date: Jul 2008
Posts: 1
#8

Re: GFCI

07/03/2008 12:35 AM

http://www.radiolocman.com/shem/shem-cache.html?di=18893

I think this article explain to what you want.

Good luck!

Best regards,

fei

Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers: