Exporting to the power grid

07/04/2008 2:01 PM

Connecting excess wind-generated electricity to the power grid through an import/export meter appears to be a simple task, but is there a better method if the amount of electricity to be exported is high? 100kw? 100,000kw? more?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Exporting to the power grid

07/05/2008 2:35 AM

Hello wlhaynes

If the intention that the wind-generated power is to exported, then a basic requirement is an import/export meter.

If power amounts are "Large", then a specially calibrated import/export meter is used, normally run from Current Transformers placed in the connecting phases.

Because of the importance of the calibration, such a meter is normally carefully checked for accuracy by the Supply Authority to which you intend connecting, and their Test Laboratory will "seal the Meter", so that it may not be "adjusted' later, by others.

Sometimes there are two import/export meters, one owned by customer, one by Supply Authority, and both are read each month, both meters should, of course, read exactly the same at all times.

Out of interest, your 100,000kW = 1 MW and that is not a "large amount" of power.

If you are planning a "Wind Farm" of turbine/alternators, it is very important to do the study carefully, before any ordering or installation commences.

If you are planning to lease part of your property to a "Wind Farm Operator", ensure that you don't have some onerous conditions placed upon you.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Associate

Join Date: Feb 2007
Posts: 32
#2
In reply to #1

Re: Exporting to the power grid

07/05/2008 2:42 PM

Thanks, Sparky, for the advice. Import/export meters will probably be used for my connections. I suspect the power company will charge me for the cost of their equipment on their side of the meters.

Wally

Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#3
In reply to #2

Re: Exporting to the power grid

07/06/2008 2:44 AM

I haven't found any real specific information about voltages and hertz when introducing power to the grid and if you have the time I have a couple questions.

What I think I understand is that the power already in the line will pull the introduced power into phase????? Is this true? Sounds tricky and dangerous.

Windmills produce power at 60 hertz only? Single or poly phase?

Inverters aren't used are they? If they are, aren't they a little dirty?

I appreciate any input about this.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5
In reply to #3

Re: Exporting to the power grid

07/06/2008 11:49 AM

In North America, the windmills have to produce 60Hz to connect to the network. The generator has to also control the voltage, power and power factor. This is not easy.

Depending on the type of generators you use, and the control strategy, an inverter might be needed. Various technologies are available without inverters. The inverter gives you more operation flexibility but add a few percents in losses.

The most important is to work with the utility company to make sure that the islanding phenomenon and the line protections are taken care of. One cannot safely connect to the line and start selling power. There are many aspects to consider to avoid de-stabilising the network especially when we are talking about many MW.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4
In reply to #1

Re: Exporting to the power grid

07/06/2008 11:39 AM

Sorry but you made a "small" mistake when you wrote:

"Out of interest, your 100,000kW = 1 MW and that is not a "large amount" of power."

It is actually 100MW. This is not small for a wind mill.

I agree with the rest of your comment.

Regards,

Marco

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Score 1 for Good Answer
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#6
In reply to #4

Re: Exporting to the power grid

07/07/2008 12:51 AM

Thanks Marcot--

I looked up ISLANDING PHENOM. and only found global warming pablum.

What happens when you are slightly out of phase--will the line pull it in? and is it the same for the voltage and current to be in phase?

Does the voltage have match the line exactly?

Sorry I have a ton of questions.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9
In reply to #6

Re: Exporting to the power grid

07/07/2008 9:14 AM

ISLANDING is caused by the network protections tripping and disconnecting a section of line where a generator is operating. This section is kept alive by the generator while the rest of the network is down. Your street then becomes an island of light in a dark city. This is dangerous for the utility work crew as they expect the power to be off. It can also prevent some protections to re-connect to the network as the voltage and phase relationship is not likely to be maintained between the utility and your generator.

A generator (windmill or diezel...) needs some sort of protections to disconnect from the line when the network fails.

The voltage and phase relationship to the line are important if you use a synchronous generator or an inverter. Induction generators are not sensitive to these parameters but have very little control over the power transfered. Induction generators also need to have an active network to generate power. They are less prone to islanding than synchronous generators but can still present some dangers. You have to choose between a simple technology with little control on the performances or the optimum technology that almost requires a PHD in controls to operate.

Another parameter to considers is what happens when you loose the network. If it represents a large part of your load, the windmill can over-speed and be damaged.

One has to do a cost benefit analysis to evaluate the technology that suits the application.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#7
In reply to #4

Re: Exporting to the power grid

07/07/2008 5:52 AM

Hello marcot

from me for noticing my error.

We had a teacher who used to say, when we caught him out:"Just checking to see if you're awake, lads", and I could have used that excuse, except it was my genuine inadvertent error.

Thanks for pointing it out.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#8
In reply to #7

Re: Exporting to the power grid

07/07/2008 8:56 AM

Don't worry about it. We all do these little oversight. It is always fun to point it out to somebody with your knowhow. It just like showing the teacher that we are awake...

Bye,

Marco

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#10
In reply to #8

Re: Exporting to the power grid

07/07/2008 6:24 PM

Excellent--One more if you have time.

The voltage being introduced if it is in phase and is lower or higher in potential, will it cause current to flow one way or the other? What's normal to enter power to the line?--Phase, Voltage and Amperage.

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#11
In reply to #10

Re: Exporting to the power grid

07/07/2008 6:26 PM

OOOps

Excellent--One more if you have time.

The voltage being introduced if it is in phase and is lower or higher in potential, will it cause current to flow one way or the other? What's normal to enter power to the line?--Phase, Voltage and Amperage.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#12
In reply to #11

Re: Exporting to the power grid

07/08/2008 9:13 AM

Basically, on an AC system consisting of a strong generator (utility network) and a weak synchronous generator or inverter (your generator), the current flow is the voltage difference between the two sources divided by the network impedance seen by your generator. This division is a vectorial calculation with phase angles, real and imaginary parts. This is where the real power (KW) and the imaginary power (KVAR) come from.

To connect to the line, you have to bring your generator to the line voltage and phase then close the switch. From that point on, your generator is locked to the line. If you vary the excitation, you will affect mostly the KVAR generated and some KW. If you try to change the speed of your generator, the KW will change to keep you synchronous until the maximum KW is reached (maximum mechanical phase difference) and you get a pole slip. At this point you are likely to damage something as this creates an extreme torque reversal in the machine and a proportionally destructive electrical transient.

Basically, the torque to the shaft gives you mostly KW and the excitation voltage the KVARs. You always have to work on both at the same time if you want to keep an constant power factor.

In a windmill application, you do not have much control on the torque as it mostly depends on the wind. You can use variable pitch blades to gain some control but it is limited. The control of a windmill is similar to a diesel generator made to go on line and the same regulators could probably be used with minor modifications.

For anything above 10KW you should consider three phases power as it eliminate the pulsating power obtained from a single phase generator. On large systems, this 120Hz pulsating power (torque) can become destructive and a filtering flywheel becomes too heavy.

Finally, harmonics and power factor do matter when the power generated becomes important with respect to the line you are connected to. Professional windmill fields will often have filter banks installed to keep operation at peak performances.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Off Topic (Score 5)
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#13
In reply to #12

Re: Exporting to the power grid

07/08/2008 10:01 AM

I really appreciate your time and find your answer easy to understand--Thank you.

I will try to do some reading/research until I come up with some more intelligent questions in the near future.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#14

Re: Exporting to the power grid

08/17/2008 7:15 PM

This might help.

Anytime amps exceed 400, CT metering (using a reduced current at a transformed ratio with a multiplier applied to the measurement - does not carry the actual system current in the meter) is used for a myriad of practical reasons, and the bussing and cables are sized for the actual load. The metering is essentially the same either way and is usually provided by the utility you connect to. The panel will be yours to provide. Also the utility will dictate the panel details for you.

The double metering mentioned above would be a customer owned meter panel on the customer side of the utility metering. The two readings will never be exactly perfectly matched over years of time, but in the short term should be within the stated accuracy parameters of the meters. Perfection is not an option.

Inverters are used for DC generation, yes it is usually fairly 'dirty' in sinusoidal terms.

AC generation is usually started like any other motor, and when the power source (Wind etc) adds power to the system the phase angles reverse and generation out to the grid begins, same as for any motor. The output of an inverter has some electronic phase/voltage matching circuitry usually, but once connected it acts much like the AC generation, reversing the phase angles to generate, but with a bit of a 'dirty' sine wave.

System outage sensing relays act to protect the generation facility and the grid repairmen as previously discussed in 'islanding'.

Hopefully you are planning to have a qualified contractor set this installation up for you, working with the connecting utility. This is for the sake of all that expensive equipment at stake there.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CJMcGill (1); Kilgore Trout (4); marcot (5); Sparkstation (2); wlhaynes (1)