Anonymous Poster

Drive

07/04/2008 11:13 PM

Why in AC drive or 3 phase inverter, output voltage is not measurable with respect to earth if output is of pulse width modulation ?

is it possible to draw only singe phase load from 3 phase inverter output ? if yes how?

because inveter output has only 3 terminals,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Drive

07/05/2008 2:14 AM

Hello Guest,

<"....Why in AC drive or 3 phase inverter, output voltage is not measurable with respect to earth if output is of pulse width modulation ?....">

Because the output of that AC Drive or 3 phase Inverter does not have a Neutral Point which is connected to Earth, (The Output is totally Isolated, for Safety purposes), there is no Voltage difference, which may be easily measured.

<"....is it possible to draw only singe phase load from 3 phase inverter output ? if yes how?....">

Yes.

It is NOT ADVISABLE to attempt this, as damage to the Inverter, AC Drive, connected equipment or persons may result.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2
In reply to #1

Re: Drive

07/05/2008 3:29 AM

One of the most common faults I've seen on ASD/VFD is a ground fault. Motors and entrance bodies where conductors get made up that can get damp, seem to be the culprit sometimes--The drives seem to be able to sense the moisture, because there have been many cases where we got the drive to run without doing much. It is sometimes frustrating that the megohm readings we take may seem good, but the drive doesn't like it. Then other times a motor will meg marginal and the drive will run it. These are open drip motors in hot, damp environments with A/B 1336 plus II drives. Seems like black magic sometimes.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #2

Re: Drive

07/05/2008 7:26 PM

Inverters typically use Residual Current ground fault sensing. The 3 output phase currents are measured and must sum to zero. Any deviation outside of the tolerance level causes a trip. So even if your megohm meter reads high values, if there is enough of a difference in current flow, it will still cause the VFD to trip.

So for that reason, you usually cannot use a single phase load off of the output of a VFD. It's a bad idea anyway, most 1 phase motor loads have capacitors and the PWM output will damage the caps and/or the cap charging current will damage the transistors. It's a race to see which one pops faster.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#8
In reply to #1

Re: Drive

07/08/2008 2:41 PM

WHY would you want to derive single phase from a VFD?

__________________
Tell 'em what they need to hear; not what they want to hear!
Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#9
In reply to #8

Re: Drive

07/09/2008 2:45 AM

Hello noshorts

It seems that "Guest", like so many of that anonymous name, has not bothered to check the replies, after asking the question.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Anonymous Poster
#3

Re: Drive

07/05/2008 3:30 AM

the multimeter you used for measurement can measure voltage in 50 Hz or 60Hz. But output of inverter is not 50Hz generally. Because of this you can not read measurement properly at out of 50Hz or 60Hz.

Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#5

Re: Drive

07/06/2008 8:11 PM

Hello Guest,

The first question is answered by spsrkstation.

This is for 2nd:

It is risky using one of the phase output (that will be two of the phase output actually) for a single phase load. There is already 3-ph. in / single ph. out inverters if the rated power is about 1 kW.

Reply
Active Contributor

Join Date: May 2008
Posts: 13
#6

Re: Drive

07/07/2008 2:26 AM

3 Phase PWM Drives are designed to drive closed delta connected systems. Hence phase to ground will not work properly if at all. There is one method to make this work for a limited part of your speed range...i.e. 30 Hz to 90 Hz.......on a 60Hz output...and this is to feed the output of the drive into a Delta-Y connected 1:1 transformer......

Once you have the transformer connected you can then connect your single phase load to the Y connected secondary.....

The limitation is the transformer efficieny curve will be affected by the frequency output due to the fact that the transformer is designed to operate at 60Hz....The loss may be minimal but the transformer manufacturer should be consulted so that you understand both the efficiency curve and the transformer heating curve based on operating frequency.....

__________________
Availalbe for short term contracts, by the hour, day or week to help you be successful.
Reply
Participant

Join Date: Jun 2008
Location: Pakistan
Posts: 3
#7

Re: Drive

07/07/2008 2:06 PM

`Dear ,

We can not Check votage on the Inverter out put Beacause Inverter out put Frequency is very high (0~650HZ ) .

If we check Voltage with Multimeter it is possible Multimeter OR Inverter damage ( this is espicalt applyable Lenze Inverter ).

We can not use Inverter out put Single Phase motor.