Cat Gen Set

07/06/2008 9:11 PM

Called to an asphalt plant recently,for a problem with a 200 hp 480 squirel cage blower,and a 100 hp 480 volt combustion air high pressure type blower,found both motors current draw going 1st down 30 amps then up over name plate rating and then settling down to an expected amount 210 amps ,this taking place in just a few seconds and repeating somewhat random around 30 second intervals. Both motors are driven by benshaw r7 soft starters.Voltage at line side both starters solid 479 volts at 60.5 Hz. same on load,never changing,current draws varying but equal on all 3 legs both motors.These blowers air flow are connected as the 200 hp pulls air and dust up out of the combustion/mixing chamber through a bag house and out to atmosphere 100 supplies air too same. There are other size VFSDs 10 hp 20 hp 5 hp not being effected. After seeing a good voltage and Hz from gen set looked at 200hp belting suspecting slippage, motor connected with almost a 1-1 ratio and what appeared to be under belted.As it turned out it was fixed by replacing the fuel filters on gen set? Why would that have not shown itself In Gen.output voltage/Hz.?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: May 2008
Posts: 13
#1

Re: Cat Gen Set

07/08/2008 5:07 AM

It appears that the diesel was cycling due to fuel flow problems. Some reasons why you may not have seen a change in the voltage or speed (Hz) is related to the following...

The voltage output of the generator is usually controlled by a fast electronic controller, which would compensate for any potential voltage variation due to cycling speed leading to cycling currents.....

The Hz output or speed of the generator would only have to change slightly to create the current surges that you mention....ie. if the engines normal speed is 1800, a 5% speed drop or 90 RPM would be equivalent to a 3 hz change in frequency....Depending on the sampling rate and the meter algorithum (it may have an averaging function built in to smooth out noise) the meter output may not change at all.....You would probably have to put on scope on the output of the generator to detect the speed change....

First the engine would slow down due to restricted fuel flow, which would result in currents dropping on the two motors with Benshaw soft starts (it would not effect the VFD's as they are fed internally via a DC bus and supported by brown out ride through capacitors), then when sufficient fuel was availalbe the engine would return to it's set speed...(probably 1800 rpm) resulting in the currents for the two motors increasing as the motor speeds followed the speed of the engine.....After the two motors accellerated to match the engine speed (minus slip) the currents would return to their normal state.....

Hope this helps...

Tom C

__________________
Availalbe for short term contracts, by the hour, day or week to help you be successful.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2008
Location: north east
Posts: 29
#2
In reply to #1

Re: Cat Gen Set

07/08/2008 5:34 PM

Thanks Tom,I didn't think about the meters being ,what should I say "slow",neither my Fluke or meters on gen set showed any change at all,which led me away,also they had just serviced the Gen set a week before,but apparently picked up some crud in a fuel shipment.So next time I should bring along a scope, I learn everyday,realising just how much I don't know. LOL it seems so clear now.

Helped a lot

DG

Register to Reply
Anonymous Poster
#3

Re: Cat Gen Set

07/08/2008 9:20 PM

The easy way to find this problem is via a fuel pressure gauge mounted on the filter base, you might also notice an audible change in engine sound. We always check the simple things first, fuel pressure, air filters, ect. Cat voltage regulators from 1990 on are solid state and do a very good job of maintaining voltage especially if they are permanent magnet style generators. signed "a CAT Service Manager"

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dg1258 (1); tchapman_egr (1)

Previous in Forum: facts   Next in Forum: Earth fault

Advertisement