Suitable mining supply

07/08/2008 2:55 PM

Client needs a 1800kW, 6600V motor to be driven from a relocatable generator set.We find it difficult to supply a 6600v genset, but 400V, 2500kVA generator set is available.The motor drives a hydraulic pump and load stays reasonable contant.

Question:

Will this 400v generator suffice if step up transformer gets used?

Transformer config, will Lt/Ht Star/Delta be ok for this application?

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Suitable mining supply

07/08/2008 3:54 PM

Should be OK. Not sure about your transformer config, are you sure it isn't 400V Delta / 6600V Star?

Also make sure that the generator can handle the starting load of the motor under load. Obvious things but they sometimes get missed.

You should be able to get some more information or advise from the gen-set manufacturer (or hire company if you are hiring long-term).

__________________
jack of all trades
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Suitable mining supply

07/08/2008 4:31 PM

6600V motor ??

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate
Safety - ESD - Inspect all things, keep the good things safe! New Zealand - Member - PalmerstonNorth -hub of the Manawatu.

Join Date: May 2008
Location: Australasia
Posts: 26
#3
In reply to #2

Re: Suitable mining supply

07/08/2008 6:39 PM

You should see it, it is really powerfull!

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#4

Re: Suitable mining supply

07/08/2008 8:00 PM

Hello jakbeuk

Yes, go for it.

Your transformer is a normal distribution transformer, with the HT Delta and LT Star.

You are using the transformer in reverse, but that should be fine.

Hope your pump starter is not a DOL one

Where in New Zealand is this pump located?

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Associate
Safety - ESD - Inspect all things, keep the good things safe! New Zealand - Member - PalmerstonNorth -hub of the Manawatu.

Join Date: May 2008
Location: Australasia
Posts: 26
#7
In reply to #4

Re: Suitable mining supply

07/13/2008 3:30 PM

This motor drives a hydraulic pump on one of those big mechanical shovels at an open cast mine in Aussie. My biggest problem I got is dealing with the start up current on the 400v side at start up, which works out to be close to 6400 Amps on 400V for about 20 sec. Any ideas as where we can look for a 6600Volt gererator that can do 200Amp?

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#8
In reply to #7

Re: Suitable mining supply

07/13/2008 6:19 PM

Hello jakbeuk

Please advise which State location in Australia:

  1. Western Australia
  2. Queensland
  3. Other - Advise please.

Is this an urgent job? - Advise how urgent.

Are you looking for a:

  • Temporary measure
  • Permanent measure

Do you want:

  • New equipment
  • Used equipment

Presumably you want diesel-powered alternator, if other please advise.

Any other useful information: Please advise.

In the meanwhile, have a look here: http://www.dieselgenerators.com/index.asp

If costs are no problem, please advise, as fastest way of getting it there if it is to be imported, is via charter air-freight.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#5

Re: Suitable mining supply

07/08/2008 11:45 PM

My two cents...

a) What is the running load (kva) of the motor ?

b) Is your generator "Continuous rated"? as your load factor is high?

c) Hope you are using a softstart to start the motor.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Anonymous Poster
#6

Re: Suitable mining supply

07/09/2008 2:00 AM

You will run the genset with lower cost efficiency.

Ask for support at www.mtu-online.com

Regards

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Suitable mining supply

07/13/2008 6:53 PM

I think your generator is way too small to start that load with anything other than a VFD. A soft starter will still require a much larger generator. The "rule-of-thumb" for generator sizing is for the genset kVA to be a minimum of 3X the motor kW for DOL starting and about 2X the motor kW if you use a soft starter. So you would need a minimum of a 3600kVA DG with a soft starter, 5.4kVA for DOL starting.

If however this s the only thing on your circuit and a severe drop in voltage and frequency is not a problem, then what you can do is go ahead and use the DG you have but disable the Governor during starting. That way when you start the motor, the voltage will drop and the DG will be allowed to slow down. The lower frequency will drop the current and the engine will essentially bring the motor up to speed as it responds to the voltage drop. But if you have any electronics involved in this machine, they will likely get corrupted by the varying frequency.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate
Safety - ESD - Inspect all things, keep the good things safe! New Zealand - Member - PalmerstonNorth -hub of the Manawatu.

Join Date: May 2008
Location: Australasia
Posts: 26
#10

Re: Suitable mining supply

08/25/2008 3:08 PM

Thanks to you all, your assistance is appreciated. Jak Beuk

__________________