Amps Calculation

07/15/2008 10:04 AM

power of a 3 phase (415v) motor given ,Howcan I calculate the min.and max current drawn by motor?

how can I select MPCB(amps rating) for the same ?If any thumb rule also there please tell me?

eg:.(415 V and 3KW)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#1

Re: Amps Calculation

07/15/2008 11:16 AM

The motor should have a nameplate. The FLA "Full Load Amps" should be present on this label. As far as minimum amps, consult the manufacturer or take a current reading with no load on the motor.

The actual amperage drawn by the motor is dependent on load connect to it.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Amps Calculation

07/15/2008 11:30 AM

Read section 430 of the NEC. Why would you want the minimum load? The wiring and breaker are based on the maximum from table 430.250.

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Amps Calculation

07/16/2008 3:28 AM

okey thank you,I can forget the minimum current ,but what about the max.current?

Here I am working with PLC pannel Building team.From customer we are getting only the power (watts)and voltage only of the motor .How can I design my MPCB's and contactors correspondingly?

Register to Reply
Power-User

Join Date: Feb 2008
Location: Northeast Ohio, USA
Posts: 267
Good Answers: 9
#4
In reply to #3

Re: Amps Calculation

07/16/2008 11:39 AM

As a "rule of thumb" as you asked, I would take the full load amps on the motor nameplate and multiply by 1.25 (125%). That is the number I would use for the MPCB in the motor control center.

If the FLA on the nameplate is 7.5, multiply by 1.25. The result is 9.375. I would use a minimum of 10 amp breaker for that application.

__________________
All that is necessary for the triumph of evil is for good men to do nothing. - Edmund Burke
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #4

Re: Amps Calculation

10/18/2010 11:22 PM

Can you quote the relevant NEC which justifies the selection of 125% FLA for MCCB which was quoted as up to 250% FLA in this forum

__________________
pnaban
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #3

Re: Amps Calculation

10/18/2010 2:03 PM

MPCBs are typically the IEC style adjustable thermal trip circuit breakers used in conjunction with a contactor to make up a Motor Starter package. Being that the thermal trips ARE the overload protection device, they must be set to the motor Full Load Amps. if you are designing a control panel from afar and do not have the motor nameplate FLA available to you, you can estimate it as follows (assuming a 3 phase motor):

approx. Motor FLA = W/(V x pf x Eff x 1.732)

pf = Power Factor, assume .7 if not otherwise known

Eff. = Efficiency, assume .8 if not otherwise known

So for your 3kW motor, Approx. FLA = 3000 / (415 x .7 x .8 x 1.732)

FLA = 3000/402.52 = 7.45A

Cross checked against a motor mfr. chart, 6.5A; probably their pf and Eff were better. So if you use this estimate, you should be OK for initial component sizing, but select an MPCB that has an adjustment range where this value fits in the middle.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Amps Calculation

10/18/2010 10:57 AM

Maximum current will be FLA in the nameplate,any increase will decrease the life of motor while minimum current will be the noload current,approximately 25 to 40% of FLA. But donot forget the locked rotor current or starting current(6In) which should not last for long.

__________________
pnaban
Register to Reply