LV switchgear busbar size

07/15/2008 10:07 AM

We want to have a LV SWGR with two sections (and a bus tie between two sections). Necessary requirement for One section is "800A, 50kA-1sec" , for the other is "2500A, 50kA-1sec". What will be the sizes of busbars?

( The size of busbar for 2500A will be greater. So, short circuit strength will be greater than 50kA-1sec. but how much? )

could you please introduce the relative standards (IEC, IEEE, ...)?

Thanks.

Register to Reply
Pathfinder Tags: LV switchgear busbar size
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: LV switchgear busbar size

07/15/2008 10:30 PM

I assume as follows

Left hand side (LHS)-- incomer 800 Amps

Right hand side (RHS) Incomer 2500 Amps

Bus tie 2500 Amps

Then both buses to be rated for 2500 Amps.

If Bus tie is 800 Amps then LHS bus to be rated for 800 Amps and RHS bus to be rated for 2500 Amps

All the buses to be rated for 50kA for one sec.

How did you arrive at the 50 kA,have done the short circuit calculation.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Member

Join Date: Jul 2008
Posts: 9
#3
In reply to #1

Re: LV switchgear busbar size

07/17/2008 12:28 AM

Thanks for your reply.

50kA-1sec is the client requested spec (acc to his consultant short circuit calculation).

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#2

Re: LV switchgear busbar size

07/16/2008 9:29 AM

Check the "Copper Development Association" at http://64.90.169.191/applications/electrical/homepage.html.

They provide some information on busbar sizing for AC and DC applications. (along with copper pipe, architectural uses, brazing info, etc.)

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Score 1 for Good Answer
Member

Join Date: Jul 2008
Posts: 9
#4
In reply to #2

Re: LV switchgear busbar size

07/20/2008 1:25 AM

Thanks for your reply.

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

am.at (2); ramvinod (1); Ried (1)

Previous in Forum: Amps Calculation   Next in Forum: Calculating Amperage

Advertisement