Calculating Amperage

07/15/2008 10:55 AM

How do I calculate the amperage when going from 1ph to a 3ph converter?

I know the amperage draw on the single phase motor. What is the difference?

__________________
The world would be a better place if we all remember to "pass it forward"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Calculating Amperage

07/15/2008 11:26 AM

Are you trying to run a 3 phase motor on single phase power using a converter?

If you want to compare single phase a 3 phase motor loads look in the NEC table 430.249 and 430.250

Register to Reply
Active Contributor

Join Date: Jul 2008
Location: Layton, Utah USA
Posts: 21
Good Answers: 2
#2

Re: Calculating Amperage

07/15/2008 11:43 AM

The difference is the (square root of 3) 1.73... That is not factoring in any heat losses and such witch is usually minmal. If you are using a VFD for the conversion it is usally recommended to double the size of drive (5hp single phase - 10 hp VFD to the three phase 5hp motor)

Register to Reply
Member

Join Date: May 2008
Location: Milwaukee, WI
Posts: 9
#3

Re: Calculating Amperage

07/15/2008 1:31 PM

Yes, the customer would like to run a 3ph motor with a 1ph service.

If the 3ph motor usually needs a 40amp dual-element fuse or a 60amp thermalmagnetic circuit breaker (under normal conditions): how do you know what he needs when using w/a 1ph service and transformer?

Thanks for your replies!

__________________
The world would be a better place if we all remember to "pass it forward"
Register to Reply
Active Contributor

Join Date: Jul 2008
Location: Layton, Utah USA
Posts: 21
Good Answers: 2
#4
In reply to #3

Re: Calculating Amperage

07/15/2008 3:07 PM

I have installed many VFD's for this application.... Just a word of advice Rotary phase converters are usally not the best solution, in fact very seldom. Just for the fact that the VFD's do a much better job, are more efficient, and almost zero maintenance once set up.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5

Re: Calculating Amperage

07/15/2008 10:54 PM

The constant in the conversion is power (kva). For single phase, KVA = V x A. For 3 phase, KVA = V x A x √3. Since the converter does not store power,

KVAin = KVAout

Thus, V1ph x A1ph = V3ph x A3ph x √3

Solving for current:

A1ph = A3ph x √3 x (V3ph / V1ph)

To input current for a given output load:

A3ph = (A1ph / √3) x (V1ph / V3ph)

Bear in mind that a Variable Frequency Drive will vary the voltage as the frequency changes to maintain a constant volts/hertz ratio. If your converter is a VFD, actual output voltage is not constant, and must be measured or calculated for the various frequencies in use in order for your calculations to be accurate.

To be really accurate, you need to consider the losses through the converter. However, for practical applications, the losses are usually negligible compared to the throughput.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Participant

Join Date: Jul 2008
Posts: 3
#6

Re: Calculating Amperage

07/16/2008 2:40 AM

Should we also considere the powerfactor in calculating the 3 ph curent...

Register to Reply
Power-User

Join Date: Feb 2008
Location: Northeast Ohio, USA
Posts: 267
Good Answers: 9
#7

Re: Calculating Amperage

07/16/2008 11:58 AM

This is not an easy question. I have furnish many control panels using the VFD to provide the three phase current. Here is the way I do it.

First, the three phase motor is does not distinguish where its driving current is produced. If the motor has a FLA of 30 amps, it will draw 30 amps regardless of where it gets the current. That is not the problem, however.

As has been posted earlier, the VFD 1) must be sized to twice the current rating of the motor FLA and 2) puts out a very clean, constant poewer to the motor. With this in mind, the VFD will protect the motor, so there is no need for a circuit breaker before the motor. There must be protection ahead of the VFD.

The solution, then is this:

1) - Select a VFD that is at least twice the current carrying capacity as the FLA of the motor and then...

2) - Select a circuit breaker to protect the VFD that is at least equal to the maximum current the VFD can accommodate.

__________________
All that is necessary for the triumph of evil is for good men to do nothing. - Edmund Burke
Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

danek (1); maheshaprasad (1); pwr2thepeople (1); sparkybust (2); The Commoner (1); wareagle (1)

Previous in Forum: LV switchgear busbar size   Next in Forum: 70 watt sodium vapour lamp

Advertisement