we have total connected laod is 250hp,actual load is 120hp now we request you to kindly suggest the suitable d.g. set for us

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: d.g.set selction

07/28/2008 10:58 PM

we have total connected laod is 250hp,actual load is 120hp now we request you to kindly suggest the suitable d.g. set for us

160 KVA will be good enough. Max motor you can start of 50HP having star-delta starter.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2
In reply to #1

Re: d.g.set selction

07/28/2008 11:48 PM

In my opinion even 125 kVA set will suffice,provided the loads are smaller.

On a 160 kVA DG set you can easily start 80 hp motor on dol mode and 120 hp on star delta mode and not as mentioned.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Member

Join Date: Jul 2008
Posts: 7
#3

Re: d.g.set selction

07/29/2008 6:49 AM

the approximations given by respected members are quite fine for more selective choice all u need to check the power factor and the required kva.suppose u have power factor of 0.7 than for connected load of 120 hp the kva=120*.750/.7.also u need to specify the individual maximum load.